Back-UPS RS1500 switches to Batery even with AC connected and detected.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS RS1500 switches to Batery even with AC connected and detected.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:41 AM . Last Modified: ‎2024-03-26 11:28 PM

0 Likes
4
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:41 AM . Last Modified: ‎2024-03-26 11:28 PM

Back-UPS RS1500 switches to Batery even with AC connected and detected.

Hello, I have an issue with my BackUps 1500. 

When I power it on, it switches to Battery. No matters if it is connected to AC or not. I also notice an electric hi-frequency buzz (not from buzzer but from circuit itself). PowerChute reports a variable AC input between 184 and 207 Volts but using calibrated instrumental i measure stable 225 Volts.

Since I am an electronic technician, I replaced capacitors and checked welds with no results.

I tried powering the UPS on and removing batteries during autocheck. It lights the replacement led. Then I plugged batteries in again. It turns led off and stays online. Then if I remove AC cord, it switches to battery again and wont go back online while AC power is restored.

As an additional information: While Online, powerchute shows AC power accurately. It changes to variable as it told above when it is on battery mode.

I appreciate any idea or info about this issue.

Tnx

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:41 AM . Last Modified: ‎2024-03-26 11:28 PM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:41 AM . Last Modified: ‎2024-03-26 11:28 PM

Which exact Back-UPS model do you have? From the description and capacity, I'm guessing it's the white plastic tower model.

If so, all I can tell you is that these things seem to be very failure prone. Every one of these that I've had has failed, and most of them failed in this exact manner. (One suffered a failure of a surface mounted 7812 voltage regulator, which rendered it completely dead.) Setting the sensitivity to "low" will buy you some time, but affords moderately less protection for attached loads and ultimately, even this is not enough.

I feel pretty confident that something is drifting out of tolerance, though what it is I'm not sure. I would have guessed capacitors, but you've mentioned replacing them. All of mine are 120 volt models (since I'm in the US). I never did think to check what, if any, incoming voltage value was reported by the UPS. As best I remember, I've since scrapped the afflicted units.

I really wish that APC and Schneider Electric would provide schematics and service literature, even if only for older and retired models, to those of us who know what we're doing.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:42 AM . Last Modified: ‎2024-03-26 11:28 PM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:42 AM . Last Modified: ‎2024-03-26 11:28 PM

I have no history of this equipment but it was working properly until it needed battery replacement. When this was done, it started having this issue.

Is there a way to get a Log from the UPS itself? Sadly, user had no powerchute or similar installed.

tnx in advance.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:41 AM . Last Modified: ‎2024-03-26 11:28 PM

0 Likes
0
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:41 AM . Last Modified: ‎2024-03-26 11:28 PM

Which exact Back-UPS model do you have? From the description and capacity, I'm guessing it's the white plastic tower model.

If so, all I can tell you is that these things seem to be very failure prone. Every one of these that I've had has failed, and most of them failed in this exact manner. (One suffered a failure of a surface mounted 7812 voltage regulator, which rendered it completely dead.) Setting the sensitivity to "low" will buy you some time, but affords moderately less protection for attached loads and ultimately, even this is not enough.

I feel pretty confident that something is drifting out of tolerance, though what it is I'm not sure. I would have guessed capacitors, but you've mentioned replacing them. All of mine are 120 volt models (since I'm in the US). I never did think to check what, if any, incoming voltage value was reported by the UPS. As best I remember, I've since scrapped the afflicted units.

I really wish that APC and Schneider Electric would provide schematics and service literature, even if only for older and retired models, to those of us who know what we're doing.

Reply

Link copied. Please paste this link to share this article on your social media post.

lmstearn_apc
Ensign lmstearn_apc
Ensign

Posted: ‎2021-06-28 06:42 AM . Last Modified: ‎2024-03-26 11:28 PM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:42 AM . Last Modified: ‎2024-03-26 11:28 PM

Better software and logging as well. Good idea to have a lifetime history- if nothing more than dates and warnings and error codes. If the UPS has ever been hit by a surge, there's nothing to say (at least on mine, 700G) it ever was, and to the extent of the impact.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:42 AM . Last Modified: ‎2024-03-26 11:28 PM

0 Likes
0
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:42 AM . Last Modified: ‎2024-03-26 11:28 PM

I have no history of this equipment but it was working properly until it needed battery replacement. When this was done, it started having this issue.

Is there a way to get a Log from the UPS itself? Sadly, user had no powerchute or similar installed.

tnx in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:42 AM . Last Modified: ‎2024-03-26 11:28 PM

0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:42 AM . Last Modified: ‎2024-03-26 11:28 PM

Hi! tnx for your answer.

Indeed, it is the white plastic tower mode. The only model reference i see is "Back-UPS RS 1500" there is no other mention on any other place. it is 120/220V dual input.

Sensitivity is set to LOW but nothing changes.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of