Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2024-11-01 09:59 AM
Hi,
I bought a Back-UPS RS 900G , and connected my server to it.
For some reason, the APC is reporting only continiously usage load of 4% / 22 watt , which isnt correct as when Im doing load tests, the CPU and spinning HDD's make up to more wattage.
I connected a Tasmoto smart plug so that the connection is:
Server --> Smart plug --> APC
The smart plug reports peak usage of 200watt and goes up and down a lot based on the load, yet the APC reports only 4% / 22 wattage
Im reading this value diretly from the screen of the APC, not via any tools
What can it be?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2024-11-01 02:24 PM
What does the APC Power Chute Software indicate while the server is running?!?
If you still have incandescent bulbs say 100 watts. Connect at least 100-300 watts and report back what the LCD indicates vs PCPE Software.
Only connect this resistive load while you test! 👍
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.