Back-UPS RS 1500 (230v) Overload Problem

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS RS 1500 (230v) Overload Problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:46 PM . Last Modified: ‎2024-03-26 01:01 AM

0 Likes
4
3898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:46 PM . Last Modified: ‎2024-03-26 01:01 AM

Back-UPS RS 1500 (230v) Overload Problem

Ok. I just got this item last January 1, 2008.

I've been banging my head on what to do with it. Today when I switched it on the overload LED flashed. Continuous alarm went off. I followed the instructions in the manual:

1.Take out everything plugged in on the battery backup, and everything else except the main power.
2.Turned off the unit.
3. Pushed the reset button on the back of the unit.
4. Powered it on.

Still the overload LED keeps coming up and the alarm goes up.

Did the whole process many times. I even unplugged the battery. Then re-plugged it.

Still the same thing.

Only the overload LED is flashing. When I power-up the unit, the self test will not proceed and will flash the overload LED.

The power surge output are working. Only the battery backup outlet are not working.

What was plugged in to the unit before the problem:

1x PC with Intel Core Duo 945
550w Coolermaster PS
1x 80g Seagate SATA
1x 160g Seagate SATA
6800gs NVidia card
Striker extreme board.

1x 19' CRT monitor

1x Linksys WRT350N wifi

The equipments are still working properly. they are now plugged in directly to the wall socket. The RS-1500 has always been plugged directly to the wall socket. I tried another wall socket no dice.

Can anyone guide me what else should I do?

Thank you!

Message was edited by: Toink

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 1500
  • 230
  • br1500i
  • rs
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:46 PM . Last Modified: ‎2024-03-26 01:01 AM

0 Likes
0
3898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:46 PM . Last Modified: ‎2024-03-26 01:01 AM

I just had a chat with customer support. They will pick-up the item and replace it with a new one free of charge.

Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:46 PM . Last Modified: ‎2024-03-26 01:01 AM

0 Likes
0
3899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:46 PM . Last Modified: ‎2024-03-26 01:01 AM

I just had a chat with customer support. They will pick-up the item and replace it with a new one free of charge.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:46 PM . Last Modified: ‎2024-03-26 01:01 AM

0 Likes
0
3898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:46 PM . Last Modified: ‎2024-03-26 01:01 AM

Hello,

If it's doing it with no load attached, and the LED is flashing, not solid, that would indicate a fault with the UPS. I recommend you have the UPS replaced.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:46 PM . Last Modified: ‎2024-03-26 01:01 AM

0 Likes
0
3898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:46 PM . Last Modified: ‎2024-03-26 01:01 AM

Thank you for your info, Notorious KMP!

So should I just drive it to their Service center then? I wonder how long I'm gonna get a replacement for this? Does anyone know if I have to bring everything, the box, accessories and all or the unit and the internal battery will do?


By the way I don't have the receipt anymore but I've check the warranty online and it says it's still under warranty - should be considering it's been only a month with me.

Thanks!

Message was edited by: Toink

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 08:46 PM . Last Modified: ‎2024-03-26 01:01 AM

0 Likes
0
3895
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:46 PM . Last Modified: ‎2024-03-26 01:01 AM

Toink,

I'm not familiar with service centers and how they operate with international units. Domestically, within the U.S. and Canada, if there is a problem with the UPS, you would have to call into Tech Support and receive a replacement via mail, eliminating service centers.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore