Back-UPS Pro 900 doesn't see the battery

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS Pro 900 doesn't see the battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-27 12:02 AM

0 Likes
7
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:30 AM . Last Modified: ‎2024-03-27 12:02 AM

Back-UPS Pro 900 doesn't see the battery

Hello world, suddenly my Back-UPS Pro 900 doesn't see the battery anymore. The LCD displays a blinking empty battery.

I checked the battery and it is fully charged (27V), powerchute personal doesn't report anything, Apcupsd says status ONLINE NOBATT, but reports BATTV 27.1V, confirming that the battery itself isn't the issue.

What can I do?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

0 Likes
0
2170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

unfortunately you have an internal problem , F06 is relay issue , maybe it cause the battery problem too,  you will need to service or replace the ups, 

regards.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

0 Likes
0
2170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

hi Pablo , you can try to clean the contacts in the batteries and the connector inside the ups , sometimes they are dirty or sometimes the cables inside the ups don't make right contact.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

0 Likes
0
2170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

Thanks Cristian, I cleaned the contacts and for some seconds I thought it was working again, because the LCD displayed a full battery, then a blinking battery symbol on the left of the battery charge indicator and then -again- the blinking empty battery

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

0 Likes
0
2170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

2 questions:

1) if you use the ups upside down , its still doing the same??

2) how old is the batteries of the ups?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

0 Likes
0
2170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

1) Upside down anything changes

2) 2 years old

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

0 Likes
0
2170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

probably you have a problem inside the ups.... if you test the battery and change date of batteries in powerchute nothing change right? and if you unplug the ups with the batteries , the ups turn off inmediately? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

0 Likes
0
2170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

Powerchute doesn't allow me to test the battery, and the ups turns off immediately.

But the news of today is a F06 error code...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

0 Likes
0
2171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:31 AM . Last Modified: ‎2024-03-27 12:02 AM

unfortunately you have an internal problem , F06 is relay issue , maybe it cause the battery problem too,  you will need to service or replace the ups, 

regards.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of