Back-UPS Pro 900 AVR and Error Light Flashing

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Back-UPS Pro 900 AVR and Error Light Flashing
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
100
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:48 PM . Last Modified: ‎2024-03-26 02:55 AM

0 Likes
2
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:48 PM . Last Modified: ‎2024-03-26 02:55 AM

Back-UPS Pro 900 AVR and Error Light Flashing

Hi,

My Back-UPS Pro 900 UPS is indicating an error which I cannot identify from any manual. The AVR indicator on the LCD is flashing together with the System Fault indicator. The UPS also then beeps 3 times every minute. No fault code is shown on the LCD display. When the AVR indicator is flashing, the indicator for low or high input power does not show.

When powered on all the systems checks are completed without error. About a minute after system checks are completed the above error starts showing up.

Input power is fine, and batteries have been replaced recently.

Any help will be appreciated.

 

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • avr
  • beeping
  • fault
  • flashing
  • system
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:48 PM . Last Modified: ‎2024-03-26 02:55 AM

0 Likes
0
2485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:48 PM . Last Modified: ‎2024-03-26 02:55 AM

On 2/11/2021 12:33 PM, Nick said:

Hi,

My Back-UPS Pro 900 UPS is indicating an error which I cannot identify from any manual. The AVR indicator on the LCD is flashing together with the System Fault indicator. The UPS also then beeps 3 times every minute. No fault code is shown on the LCD display. When the AVR indicator is flashing, the indicator for low or high input power does not show.

When powered on all the systems checks are completed without error. About a minute after system checks are completed the above error starts showing up MyLowesLife.

Input power is fine, and batteries have been replaced recently.

Any help will be appreciated.

 

Over temperature On Battery - UPS has exceeded the over temperature threshold. Note: The UPS will beep and the red LED will illuminate till the internal temperature reaches the normal range for 5 minutes before the UPS shuts down.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:48 PM . Last Modified: ‎2024-03-26 02:55 AM

0 Likes
0
2486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:48 PM . Last Modified: ‎2024-03-26 02:55 AM

On 2/11/2021 12:33 PM, Nick said:

Hi,

My Back-UPS Pro 900 UPS is indicating an error which I cannot identify from any manual. The AVR indicator on the LCD is flashing together with the System Fault indicator. The UPS also then beeps 3 times every minute. No fault code is shown on the LCD display. When the AVR indicator is flashing, the indicator for low or high input power does not show.

When powered on all the systems checks are completed without error. About a minute after system checks are completed the above error starts showing up MyLowesLife.

Input power is fine, and batteries have been replaced recently.

Any help will be appreciated.

 

Over temperature On Battery - UPS has exceeded the over temperature threshold. Note: The UPS will beep and the red LED will illuminate till the internal temperature reaches the normal range for 5 minutes before the UPS shuts down.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

knopfler19_apc
Crewman knopfler19_apc
Crewman

Posted: ‎2024-01-09 07:15 PM

0 Likes
0
1588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-09 07:15 PM

Same happened today with a “new” replacement unit. Is it correct that the cause is over-heating? Is the unit defective? At 25ºC the battery should not overheat without being working (I have had many apc in south Spain with A LOT higher ambient temp with no problems at all)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now