Back-UPS Pro 1200 randomly beeping

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS Pro 1200 randomly beeping
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:55 AM . Last Modified: ‎2024-03-27 02:19 AM

0 Likes
11
3113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:55 AM . Last Modified: ‎2024-03-27 02:19 AM

Back-UPS Pro 1200 randomly beeping

Symptoms:

  • 3 (sometimes 2) short beeps, every 30 seconds
  • system fault blinking with NO fault number displayed, just the usual Watts display
  • AVR blinking but low/high input icons are NOT lit
  • does this for 20-30 minutes and then stops
  • seems to happen every day around the same time (noon and evening)

This is quite annoying as the beeps can't be muted. Other than that the UPS works correctly.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • beeping
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
benjilaclef_apc
Crewman benjilaclef_apc
Crewman

Posted: ‎2021-06-28 02:57 AM . Last Modified: ‎2024-03-27 02:18 AM

0 Likes
0
3112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:57 AM . Last Modified: ‎2024-03-27 02:18 AM

Hello Luper, 

Thanks for your response 🙂 

I contacted my country's support, and they sent me a new one immediately, because they had never seen this problem. 

I received the remplacement model two days later, it was perfect !

Have a nice day, 

Benjilaclef

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:56 AM . Last Modified: ‎2024-03-27 02:19 AM

0 Likes
0
3112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:56 AM . Last Modified: ‎2024-03-27 02:19 AM

Hi Luper,

Could you provide us with the exact model and serial number of the unit?  A few more general questions:

How is the power quality in your area?

Have you ever replaced the battery?

What are you connecting to this unit and what is the total load percentage?

Are you using any software with this unit?

Is there anything else that occurs concurrently during these same intervals that this beeping begins?

Did this just begin recently and did any major event occurs at the inception of the issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:56 AM . Last Modified: ‎2024-03-27 02:18 AM

0 Likes
0
3112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:56 AM . Last Modified: ‎2024-03-27 02:18 AM

Model is BR1200G-FR, S/N 3B1437X01879

Power quality is OK.

Battery was never replaced, unit was bought in january.

I connect a plasma TV, 2 preamp speakers, and a satellite decoder. Load is around 20%.

No software.

Nothing else occurs during the beeps. Also note that they occur indiferently wether the TV is on or off.

It begun maybe 3 weeks ago.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:56 AM . Last Modified: ‎2024-03-27 02:18 AM

0 Likes
0
3112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:56 AM . Last Modified: ‎2024-03-27 02:18 AM

Are you sure it is not 4 beeps every 30 seconds?

I would recommend unplugging the unit from utility power, unplugging the equipment plugged into the unit, removing the battery, and holding the power button for 20 seconds.  Then reassemble the unit and power it back on and observe its behaviour.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:56 AM . Last Modified: ‎2024-03-27 02:18 AM

0 Likes
0
3112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:56 AM . Last Modified: ‎2024-03-27 02:18 AM

Yes, 3, not 4.

I will try your recommendation, thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:56 AM . Last Modified: ‎2024-03-27 02:18 AM

0 Likes
0
3112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:56 AM . Last Modified: ‎2024-03-27 02:18 AM

It didn't help, problem still persists.

Please note that it does 3 *short* beeps, shorter than the 4 ones you get when on battery power.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:56 AM . Last Modified: ‎2024-03-27 02:18 AM

0 Likes
0
3112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:56 AM . Last Modified: ‎2024-03-27 02:18 AM

Luper,

As this is a unit used in France, I would advise calling into your local support for further troubleshooting.  From what you described, this may be an issue/indicator that is specific to the French unit.

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:56 AM . Last Modified: ‎2024-03-27 02:18 AM

0 Likes
0
3112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:56 AM . Last Modified: ‎2024-03-27 02:18 AM

Hello,

Luper, have you found a solution ? Mine go exactly the same way : 3 Beeps every 30s, "AVR" and "Go Manuel" ( Systeme Fault) blinking without Fxx.

Reply

Link copied. Please paste this link to share this article on your social media post.

benjilaclef_apc
Crewman benjilaclef_apc
Crewman

Posted: ‎2021-06-28 02:57 AM . Last Modified: ‎2024-03-27 02:18 AM

0 Likes
0
3112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:57 AM . Last Modified: ‎2024-03-27 02:18 AM

Hello, 

I've exactly the same problem like you, with a French model like Luper. This is a new one that I installed yesterday, it works for 1 hour with no problem, and after it make 3 Beeps every 30/40s, with "AVR" and "SystemeFault" blinking and no number of error (no Fxx)

How can I do ? 

Thanks, 

Benji

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:57 AM . Last Modified: ‎2024-03-27 02:18 AM

0 Likes
0
3112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:57 AM . Last Modified: ‎2024-03-27 02:18 AM

Hii, you can do it very easily don't worry about that.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:57 AM . Last Modified: ‎2024-03-27 02:18 AM

0 Likes
0
3112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:57 AM . Last Modified: ‎2024-03-27 02:18 AM

Since the support has no answer, I ended opening the APC and removing the beeper from the PCB with a pair of pliers (a black cylinder with a hole on top), no more beeps and it works (apart from the beeps it always worked fine). 

(and sorry but "contact your country's support" is not an acceptable answer from a multinational company, you should have contacted them yourself, I already did my part of the job by investing time in reporting an issue) 

Reply

Link copied. Please paste this link to share this article on your social media post.

benjilaclef_apc
Crewman benjilaclef_apc
Crewman

Posted: ‎2021-06-28 02:57 AM . Last Modified: ‎2024-03-27 02:18 AM

0 Likes
0
3113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:57 AM . Last Modified: ‎2024-03-27 02:18 AM

Hello Luper, 

Thanks for your response 🙂 

I contacted my country's support, and they sent me a new one immediately, because they had never seen this problem. 

I received the remplacement model two days later, it was perfect !

Have a nice day, 

Benjilaclef

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore