Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Back-UPS Pro 1000 Dies!

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS Pro 1000 Dies!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
147
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

0 Likes
6
3893
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

Back-UPS Pro 1000 Dies!

We just bought a new Back-UPS Pro 1000 from our local Office Depot. This UPS is connected to my Desktop Dell, Flat Screen Monitor and Sound Speakers. A total load of 21% average. The UPS ran well for about a week when we heard a bunch of clicking noises and after a bit a number of beep-beeps. The Dell died mid use. We looked at the display on the UPS and it said the battery was 0% and kept beeping. Our 120vac was live and had not dropped out at any time. We don't know how long the clicking was. The beeping started right when the UPS died.
The day before this happened we plugged this UPS in to a brand new outlet strip with surge protection. It was tough to plug the UPS in directly to the outlet behind the desk. When we plugged the UPS in that new outlet strip, we heard a pop and the breaker tripped in the house. The outlet strip was a dead short at the plug end. That outlet worked before we plugged the UPS in. We then plugged the UPS back into the wall outlet and it was fine. We returned the outlet and never used any other outlet. Even after that the UPS seemed to work great for a day until the clicking and died. I took the battery pack out and re-inserted it again. The UPS recharged the battery to 100% and it seemed to run. Because we did not trust it, we took it back to Office Depot and replaced it with the same model UPS. We hope this was a one time problem.
After hearing all of the info... Any ideas on the cause of the UPS dying?
Could the UPS cause the surge protected outlet to short out? WHY?
Could the bad surge protected outlet have caused the UPS to die out a day later? WHY?
Has anyone else had a similar problem?
The replaced UPS is still running after 24 hours.
What do you think????
TNX

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

0 Likes
0
3893
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

Nope... The battery was turned over and inserted into the proper orientation. It charged up ok and looked good until the time it went to backup (both times). As I said before, we reinserted the battery back in and waited for the complete charge. For the last week now it's been working great. I don't get it. I hope it all stays that way.
TNX

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

0 Likes
0
3893
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

We just bought a new Back-UPS Pro 1000 from our local Office Depot. This UPS is connected to my Desktop Dell, Flat Screen Monitor and Sound Speakers. A total load of 21% average. The UPS ran well for about a week when we heard a bunch of clicking noises and after a bit a number of beep-beeps. The Dell died mid use. We looked at the display on the UPS and it said the battery was 0% and kept beeping. Our 120vac was live and had not dropped out at any time. We don't know how long the clicking was. The beeping started right when the UPS died.
The day before this happened we plugged this UPS in to a brand new outlet strip with surge protection. It was tough to plug the UPS in directly to the outlet behind the desk. When we plugged the UPS in that new outlet strip, we heard a pop and the breaker tripped in the house. The outlet strip was a dead short at the plug end. That outlet worked before we plugged the UPS in. We then plugged the UPS back into the wall outlet and it was fine. We returned the outlet and never used any other outlet. Even after that the UPS seemed to work great for a day until the clicking and died. I took the battery pack out and re-inserted it again. The UPS recharged the battery to 100% and it seemed to run. Because we did not trust it, we took it back to Office Depot and replaced it with the same model UPS. We hope this was a one time problem.
After hearing all of the info... Any ideas on the cause of the UPS dying?
Could the UPS cause the surge protected outlet to short out? WHY?
Could the bad surge protected outlet have caused the UPS to die out a day later? WHY?
Has anyone else had a similar problem?
The replaced UPS is still running after 24 hours.
What do you think????
TNX

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

0 Likes
0
3893
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

Well..... Here we are again...
The same problem again....
Today the same UPS was running great for around 1.5 weeks until the UPS started to beep beep AGAIN. It's a fast two beeps and the two beeps are about a second apart. BTW the manual doesn't say anything about a double beep one second apart. The battery shows fully charged. The display says its online with 118 volts. Not battery mode. We tried to reset it. Tried turning it off and back on. Still beep beep and it's online. Turned it off for about 7 hours with nothing connected. After 7 hours of off time and nothing connected to it, we turned it back on. The battery is now almost drained!!! Still no load, nothing connected and it was off! It's now on and it seems to be recharging! Now the only thing we remember that may have something to do with it is, two days ago we lost power and the UPS did what it should. It keep the computer up and running until we shut it down a few minutes later. Power came back after about 15 minutes. It's been running great until today's trouble.
Any ideas on what the heck is going on with this? I don't get it at all. Has anyone ever heard about this problem or what the two beep beeps mean?
TNX

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

0 Likes
0
3893
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

Thanks Much.
I just received a call from my wife that the same model replacement UPS is now beeping and draining the battery. Same as before! About the same number of days before it dies out! The power to the outlet is there but the UPS will not come out of battery backup mode. What the heck! I will need to bring this one back also! We are not using it in any way different than anyone else. I'm lost. I've always liked APC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

0 Likes
0
3893
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

One more bit of info....
After the beeping and the UPS stays in battery backup mode we turn it back off. Pull the battery pack out and plug the battery pack back in. Turn on the UPS and it starts charging the battery back up and it works ok. I don't know for how long though. It may die again in a hour or a day. Who knows.
It's weird I'm the only guy this happens too.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

0 Likes
0
3893
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

Yep.
2 short beeps then about 2-3 seconds between beeps. It did this until it finally dies 20-30 minutes later. This was the first one.
The second one has the same 2 beeps 2-3 seconds between beeps. This time my wife was there and noticed the beeps when it started. The battery was full but it had switched over to battery backup. The outlet was active.
TNX

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

0 Likes
0
3894
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:18 AM . Last Modified: ‎2024-03-21 11:58 PM

Nope... The battery was turned over and inserted into the proper orientation. It charged up ok and looked good until the time it went to backup (both times). As I said before, we reinserted the battery back in and waited for the complete charge. For the last week now it's been working great. I don't get it. I hope it all stays that way.
TNX

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore