Back-UPS ES 8 Outlet 350VA 120V (6 & 8 Slot) Issues

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS ES 8 Outlet 350VA 120V (6 & 8 Slot) Issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:04 PM . Last Modified: β€Ž2024-03-25 11:45 PM

0 Likes
5
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:04 PM . Last Modified: β€Ž2024-03-25 11:45 PM

Back-UPS ES 8 Outlet 350VA 120V (6 & 8 Slot) Issues

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=BE350R&tab=features

Our company is having problems with this (as well as the 6 slot variety) kind of battery.

We have computers and monitors connected to the "Battery Backup & Surge Protection" slots on these APC batteries, but during an outage, computers go down. We have it set up so there are only 2 computers maximum to one of these Backup batteries, so I'm not sure if its an overloading problem. In one case, we have two computers connected to one battery, and they both stayed online.

Some of our computers go down, some don't. What can we do to fix the problem? We only need our computers and monitors to stay on during a power outage.

Also wanted to know if there is an easy way to test out your batteries when there isn't a power outage (like do we just unplug your batteries from the outlets or not?).

Message was edited by: agvsport

UPDATE:

Another power outage occurred. I was able to save 2 computers that previously powered out during a storm (I moved their Monitor power chords from "Backup Battery & Surge Protection" to "Surge Protection", each of these PCs have their own separate Backup batteries).

I also found that two groups of two PCs connected to one Back-UPS ES 8 Outlet 350VA 120V (8 slot) Battery each caused all four to power out. With only one computer per Back-UPS ES 8 Outlet 350VA 120V (8 slot) Battery, I was able to save 2 out of the 4 during the power outage.

However, there is now a new problem that didn't exist before. There are two PCs (and their Monitors) connected to a Back-UPS XS 1000 (8-slot, http://www.apc.com/products/family/index.cfm?id=23). One of the two we have set up as a backup PC for the other PC. The Backup PC stays online, while the other didn't.

Message was edited by: agvsport

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:04 PM . Last Modified: β€Ž2024-03-25 11:45 PM

0 Likes
0
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:04 PM . Last Modified: β€Ž2024-03-25 11:45 PM

I have a my computer, LCD monitor and printer attached to the Battery Back up plus surge protector and three other accessories attached to the surge protector only. So far, today, my computer, LCD and printer keeps shutting down while the others remained on. I have the same kind of UPS 350VA (8 slot). I didn't upload the software on my computer yet. I just set up everything two days ago. Now, I had to unplug everything from the back up because my computer keeps turning on and off while plug into this UPS unit. Could it be a faulty unit?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:04 PM . Last Modified: β€Ž2024-03-25 11:45 PM

0 Likes
0
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:04 PM . Last Modified: β€Ž2024-03-25 11:45 PM

Greeetings agvsport!

It certainly appears that your issue with extremely short runtime is caused by excessive load on the 350VA UPSs as well as the likelihood that the batteries (at least those in the BE350U 6 outlet varieties) are old. These UPSs have a 200W maximum capacity, which is easily exceeded (as you discovered) by connecting two modern PCs plus displays to the battery-backup outlets.

These are the lowest capacity UPSs in our entire product line-up, and they are intended for use with one basic PC. An easy way to prove that it's a load issue would be to plug just one PC tower into the UPS and disconnect the UPS from the wall, forcing it on-battery. You should get some measure of on-battery runtime.

With brand new batteries at full charge, these UPSs would provide approx 10min at half load (100W) and just under 3min at full load (200W).

Are the monitors heavy glass CRT displays or flat panel LCD type? The CRT displays certainly draw too much power from the battery in conjunction with the tower PC.

As far as the issue on the BX1000, if both are definitely plugged into the outlets marked battery-backup and one did stay running during the outage, the other PC may be incompatible with the type of power this UPS supplies when running off the battery.

An easy test would be to connect the PC that turned off into the UPS' battery protected outlets all by itself and pull the UPS' plug from the wall. If the computer shuts down or reboots, it may not be compatible with the transition time from AC power to Battery, or the output AC waveform.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:04 PM . Last Modified: β€Ž2024-03-25 11:45 PM

0 Likes
0
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:04 PM . Last Modified: β€Ž2024-03-25 11:45 PM

Thank you for responding JoeMomma πŸ™‚

Would first like to say that I fixed three more computers. I connected two computers and their monitors to a CyberPower 550VA battery. The battery works fine. The third computer I connected to one of the Back-UPS ES 350 (8-slot) batteries. This battery works fine with this one PC as well. Their is a fourth computer that I tried with a set-up exactly like the third one (Its singly connected to a Back-UPS ES 350 (8-slot) battery), however it doesn't work 😞

All the monitors (minus our one mac, which is one of the computers powering out during a storm) are flat panel monitors.

Idunno why one of the two PCs connected to the BX1000 would power out and the other doesn't. Hardware-wise, the only difference they have is that one of the PCs is an XPS 200 (thats the PC that powers off) and the other is a Dell Pentium 4 Processor (which doesn't power off). All the other PCs in the office are Dell Pentium 4 Processors, minus the Mac. The hardware difference may be the problem. I will try that trick you mentioned in your last paragraph on the XPS 200.

Some of these batteries may not be able to power a single computer. We most likely will need to buy some new ones or get the old ones fixed.

I'll update this thread with my progress as I continue to try to fix this problem.

Message was edited by: agvsport

Message was edited by: agvsport

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:04 PM . Last Modified: β€Ž2024-03-25 11:45 PM

0 Likes
0
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:04 PM . Last Modified: β€Ž2024-03-25 11:45 PM

Another very simple test of the UPS is to connect a 100W lamp to the UPS. Then unplug the UPS from the wall. I've already provided the runtime that you would get with a 100W load with a fully charged, brand-new battery. Based on the result of this test, you will be able to determine just how aged your battery is based on runtime performance.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:04 PM . Last Modified: β€Ž2024-03-25 11:45 PM

0 Likes
0
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:04 PM . Last Modified: β€Ž2024-03-25 11:45 PM

Bittersun,

Did you hear any beeping from the UPS when you experienced these difficulties?

Perhaps you can also try to limit what is plugged into the battery side (perhaps just plug the LCD only) for testing purposes. If the UPS performs better, the issue is likely load-related.

What kind of computer and printer do you have?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:04 PM . Last Modified: β€Ž2024-03-25 11:45 PM

0 Likes
0
892
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:04 PM . Last Modified: β€Ž2024-03-25 11:45 PM

I have a my computer, LCD monitor and printer attached to the Battery Back up plus surge protector and three other accessories attached to the surge protector only. So far, today, my computer, LCD and printer keeps shutting down while the others remained on. I have the same kind of UPS 350VA (8 slot). I didn't upload the software on my computer yet. I just set up everything two days ago. Now, I had to unplug everything from the back up because my computer keeps turning on and off while plug into this UPS unit. Could it be a faulty unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore