Back UPS ES 725 only providing 37V when on Battery Power

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back UPS ES 725 only providing 37V when on Battery Power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

0 Likes
7
1689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

Back UPS ES 725 only providing 37V when on Battery Power

I bought this UPS (ES 725) from Microcenter less than a year ago and we haven't had any power problems while I've been home. When it does go off it usually stays off long enough to drain the batteries on our other APC units (two LS 700's that we'vve had for years) so I just assumed this one has been working. I just found out last night that when it switches to battery power my computer system goes dead immediately. I've checked the connections on the battery, and tested the DC voltage of the battery (13.6V) and the Powerchute says the battery is fully charged. I've done the checks in the KB article and everything works, except that when it does switch to battery power it is only providing 37V at the outlets on the UPS. I've tried disconnecting everything and only running a lamp with a 40W bulb and this doesn't work either. When I measured the voltage at the outlets on the UPS everything was disconnected and the unit was on battery power. Any ideas? I don't have the receipt anymore so I don't know the exact date I bought it, but it was sometime around Christmas 2006.

Roger

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

0 Likes
0
1690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

Does the UPS emit the 4 beeps every 30 seconds while it is on battery? Have you tried just reconnecting the internal battery leads?

You may want to try reconnecting the internal battery, and then powering the UPS on its own battery power. To do this, make sure the UPS is off and unplugged. With the battery connected, push and hold the On button until you hear a short beep, followed by a second longer sustained beep. During the second sustained beep, let go of the button. The UPS should power up on its own battery power. Try a lamp in the battery backup outlets while in this state.

How old is the battery? What is the serial off of the UPS, and is it the original battery?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

0 Likes
0
1690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

Thanks for the help Sarge. I'll give tech support a call. Will it be a problem if I don't know my exact purchase date? I no longer have the receipt.

Roger

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

0 Likes
0
1690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

I bought this UPS (ES 725) from Microcenter less than a year ago and we haven't had any power problems while I've been home. When it does go off it usually stays off long enough to drain the batteries on our other APC units (two LS 700's that we'vve had for years) so I just assumed this one has been working. I just found out last night that when it switches to battery power my computer system goes dead immediately. I've checked the connections on the battery, and tested the DC voltage of the battery (13.6V) and the Powerchute says the battery is fully charged. I've done the checks in the KB article and everything works, except that when it does switch to battery power it is only providing 37V at the outlets on the UPS. I've tried disconnecting everything and only running a lamp with a 40W bulb and this doesn't work either. When I measured the voltage at the outlets on the UPS everything was disconnected and the unit was on battery power. Any ideas? I don't have the receipt anymore so I don't know the exact date I bought it, but it was sometime around Christmas 2006.

Roger

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

0 Likes
0
1691
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

Does the UPS emit the 4 beeps every 30 seconds while it is on battery? Have you tried just reconnecting the internal battery leads?

You may want to try reconnecting the internal battery, and then powering the UPS on its own battery power. To do this, make sure the UPS is off and unplugged. With the battery connected, push and hold the On button until you hear a short beep, followed by a second longer sustained beep. During the second sustained beep, let go of the button. The UPS should power up on its own battery power. Try a lamp in the battery backup outlets while in this state.

How old is the battery? What is the serial off of the UPS, and is it the original battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

0 Likes
0
1690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

I did remove and check the battery leads, and I also used some electrical contact cleaner on the terminals of the battery. The battery is the original battery that was supplied with the unit. I tried the part about powering on the unit while holding the power button, but I never got the second long beep. Could this be because I have all alarms/beeps disabled through powerchute? I will reconnect it to my system and enable the alarms to make sure. I do have the green "on" LED on steadily, I just assumed this indicated that the unit is under power from the battery. When it is in this state, I measure ~37V AC on the battery powered outlets. As soon as I plug something into another battery powered outlet, the voltage on my multimeter goes to 0.

The unit was purchased new approx. 9 months ago, and it has the original battery, which powerchute says is fully charged, and my DMM showed having ~13.4V DC. The serial is 3B0639X63372 and the unit is a BE725BB (right above the serial number).

Roger

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

0 Likes
0
1690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

I just re-enabled the alarms and tried the "cold start" process. I get the short beep and the green LED comes on. While still holding the button in, the green LED goes out for about one second and I get the 4 beeps indicating loss of power. I never get the second long beep. I even continued to hold the button long enough that 30 seconds later the 4 beeps sounded again. Nothing was plugged into the unit during this time, and it was disconnected from the wall outlet.

Roger

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

0 Likes
0
1690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:46 AM

OK, just leave the UPS in the state with the 4 beeps every 30 seconds. There may not be a second sustained beep with this model. Try plugging a lamp into the Battery Backup outlets after starting the UPS from its own battery power.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:45 AM

0 Likes
0
1690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:57 PM . Last Modified: ‎2024-03-26 01:45 AM

Nothing happens, I get no power to anything I've tried plugging into the battery powered outlets. I've tried the original computer, a lamp, and a power supply for a USB hub that has an LED power indicator on the transformer. My DMM shows only ~37V AC while it is in this state, and if I plug something into another outlet the DMM shows that the voltage drops completely to 0 volts.

Roger

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore