Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Back-UPS ES 700Y-IND bad ups or bad battery

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS ES 700Y-IND bad ups or bad battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
154
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
wstar123
wstar123
Contributor

Posted: ‎2024-06-23 03:38 PM

0 Likes
5
1486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-23 03:38 PM

Back-UPS ES 700Y-IND bad ups or bad battery

I am having issues with a recently installed Back-UPS ES 700Y-IND. The battery is giving backup & is also getting charged as far as I can tell after conducting multiple tests with around 33% load. However, everything else in the powerchute software seems to suggest otherwise. These are some of the pics.

No load connected on mains powerNo load connected on mains power

pic1: ups on mains with no load connected

 

on battery power with load connectedon battery power with load connected

pic2: ups on battery power with around 33% load

 

on battery power with load connected just before auto shutdownon battery power with load connected just before auto shutdown

pic3: ups on battery power with around 33% load just before auto shutdown

 

back to mains power & after running self testback to mains power & after running self test

pic4: ups back on mains after & after running a self test which it passed

 

data log entriesdata log entries

pic5: data log entries for above/similar scenarios

 

I don't think above stats are "normal" so what can be the reason. This unit is under warranty so I won't be opening it.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
wstar123
wstar123
Contributor

Posted: ‎2024-06-26 01:37 AM

In response to Teken
0 Likes
3
1421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-26 01:37 AM

Turned out it was the supposedly new PowerChute Serial Shutdown software which was at fault. The local technical support asked me to install PowerChute Personal Edition & upon installation it showed me all values as expected. This has been quite disappointing considering I spent days browsing the internet looking for solutions ranging from various reset procedures to testing under different scenarios with load attached when the reason was latest software. I didn't find the link of PowerChute Personal Edition on this UPS model page on APC website so assumed it is not supported by the Personal Edition software. Doesn't APC test their own software with various not so new models to at least confirm the compatibility & correct functioning of latest software?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Teken
Teken
Champion

Posted: ‎2024-06-24 05:50 AM

0 Likes
4
1444
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-24 05:50 AM

As the hardware is still under warranty it just makes sense to contact APC Technical Support to determine root cause. If the unit is determined to be faulty they will initiate a RMA for you.

 

Have the purchase receipt, serial number, and the screen captures you have here. Download the logs to see if there are any active faults / errors in the system and relay the same to APC. 

Let us know how everything turns out and the final outcome. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

wstar123
wstar123
Contributor

Posted: ‎2024-06-26 01:37 AM

In response to Teken
0 Likes
3
1422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-26 01:37 AM

Turned out it was the supposedly new PowerChute Serial Shutdown software which was at fault. The local technical support asked me to install PowerChute Personal Edition & upon installation it showed me all values as expected. This has been quite disappointing considering I spent days browsing the internet looking for solutions ranging from various reset procedures to testing under different scenarios with load attached when the reason was latest software. I didn't find the link of PowerChute Personal Edition on this UPS model page on APC website so assumed it is not supported by the Personal Edition software. Doesn't APC test their own software with various not so new models to at least confirm the compatibility & correct functioning of latest software?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2024-06-26 10:01 AM

In response to wstar123
0 Likes
2
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-26 10:01 AM

One would think, but to be fair what Power Chute software was bundled with the hardware? 🤔

 

If PCPE was included with the hardware that’s simply an oversight by you. Now, if PCSS was included with the hardware that’s absolutely on APC! 🤦‍♂️

 

Regardless, appreciate you taking the time to follow up and call out the cause and solution. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

wstar123
wstar123
Contributor

Posted: ‎2024-06-26 11:05 PM

In response to Teken
0 Likes
1
1389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-26 11:05 PM

When bundled software is mentioned people generally assume some cd/dvd bundled with the hardware as is the case with laptops & many other pc components. I now see that instruction manual in the box does mention PowerChute Personal Edition software but considering that manual was printed in Apr 2022 (as per enclosed test report) & PowerChute Serial Shutdown software being released in March 2023 it was reasonable for me to assume that Serial Shutdown software supersedes Personal Edition in terms of performance & features so it is the one to be used not to mention APC website itself only shows Serial Shutdown software link on this model product page. Now that I have confirmed that Serial Shutdown software doesn't work correctly with ES 700Y-IND model & possibly some other models too shouldn't APC technical support at least replace the Serial Shutdown software link with personal Edition with a note that though discontinued the Personal Edition is the one that works correctly for such UPS models & not the newer Serial Shutdown version. Maybe someone here can pass on this feedback to APC team.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2024-06-27 03:42 AM

In response to wstar123
0 Likes
0
1377
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-27 03:42 AM

I agree the company could do better in communicating the information as it relates to what software is applicable to a specific piece of legacy hardware. 

The APC website is truly one of the worst on the Internet! 🤢 It’s like they hired a five year old to decide what and how things should be presented and organized?!? 🤦‍♂️

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore