Back-UPS ES 500 - low voltage during blackout

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
rickapc1_apc
Crewman
Crewman
0 Likes
3
228

Back-UPS ES 500 - low voltage during blackout

This was originally posted on APC forums on 3/28/2009


I have a Back-UPS ES 500. During a blackout, the output voltage drops from 120 volts to 90 volts, and stays at 90 volts until the external power is restored a few minutes later. Shouldn't the battery outpout voltage stay constant at approx. 120 volts?
The test load is only one 60W light bulb.


Accepted Solutions
rickapc1_apc
Crewman
Crewman
0 Likes
0
228

Re: Back-UPS ES 500 - low voltage during blackout

This was originally posted on APC forums on 3/29/2009


Hi. I am using a simple voltmeter, which is most probably not a true rms-voltmeter.
I will try to get one from Radio Shack if available.
And thanks for the article included in your link. It was very useful.

The only doubt that remains for me is that the 60W light bulb gives a dimmer light when on battery power,
compared to the bright light given when the battery is connected to an electric wall outlet.
How much drop in voltage would be normal to observe when on battery power?

Thanks.

See Answer In Context

3 Replies 3
BillP
Administrator Administrator
Administrator
0 Likes
0
228

Re: Back-UPS ES 500 - low voltage during blackout

This reply was originally posted by Angela on APC forums on 3/30/2009


this UPS outputs 115v while on battery.

Cap1_apc
Lt. Commander
Lt. Commander
0 Likes
0
228

Re: Back-UPS ES 500 - low voltage during blackout

This was originally posted on APC forums on 3/29/2009


Hi,

How are you validating 90v output? Are you using a voltmeter?

Because this unit outputs a step approximated sine wave on battery, only a true RMS voltmeter will read the correct voltage while the unit is on battery. True RMS voltmeters tend to cost more $, so perhaps yours isn't?

More info here:
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=1493

rickapc1_apc
Crewman
Crewman
0 Likes
0
229

Re: Back-UPS ES 500 - low voltage during blackout

This was originally posted on APC forums on 3/29/2009


Hi. I am using a simple voltmeter, which is most probably not a true rms-voltmeter.
I will try to get one from Radio Shack if available.
And thanks for the article included in your link. It was very useful.

The only doubt that remains for me is that the 60W light bulb gives a dimmer light when on battery power,
compared to the bright light given when the battery is connected to an electric wall outlet.
How much drop in voltage would be normal to observe when on battery power?

Thanks.