Back-UPS BX1400U-MS for Corsair AX1500i Active PFC Power Supply

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS BX1400U-MS for Corsair AX1500i Active PFC Power Supply
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-26 11:27 PM

0 Likes
4
1479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-26 11:27 PM

Back-UPS BX1400U-MS for Corsair AX1500i Active PFC Power Supply

Hello guys, I want to purchase a APC Back-UPS BX1400U-MS to keep my computer safely when the event of power failure occur. My PC use Corsair AX1500i power supply, which is an Active PFC PSU. I read lots of articles on internet that complain about UPS that output stepped sine wave (or simulated) will not function property with Active PFC PSU, recommendation is buy a true sine wave UPS. So should I go with the Back-UPS?

Thanks.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-26 11:27 PM

0 Likes
0
1480
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-26 11:27 PM

Ok really appreciate for your response.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-26 11:27 PM

0 Likes
0
1481
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-26 11:27 PM

Hi Thong,

You Corsair AX1500i is rated at 1500W and by following this KBase: http://www.apc.com/us/en/faqs/FA158939/ it may have a inrush draw of 1875W. This is way beyond the capacity of the BX1400U-MS which is 700W. You may opt, at a minimum, for a Smart UPS model like an SMT2200I that have a capacity of 1980W. In addition, APFC PSUs like pure sine wave output UPS/s which a Smart...

Hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-26 11:27 PM

0 Likes
0
1481
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-26 11:27 PM

Hi Mike,

Thanks for response. Can you confirm that the inrush draw only apply with simulated sine wave or both UPS type? Because I don't want to pay more for larger UPS if it is not necessary. Can I go with SMC/SMT 1000/1500VA?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-26 11:27 PM

0 Likes
0
1481
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-26 11:27 PM

Hi Thong,

The inrush draw applies to any UPS unit even not APC. From what I have mentioned previously, the least you can get is the SMT2200I because the SMT1000I and SMT1500I are respectively 700W and 1000W capacity only/ This is beyond your PSU's 1500W rating.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-26 11:27 PM

0 Likes
0
1481
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:43 AM . Last Modified: ‎2024-03-26 11:27 PM

Ok really appreciate for your response.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore