Back-UPS 650 boots to "sleep mode" after replacing battery. Functions as inverter, but not as UPS.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS 650 boots to "sleep mode" after replacing battery. Functions as inverter, but not as UPS.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-11 10:58 PM . Last Modified: ‎2024-03-19 11:44 PM

0 Likes
2
2424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:58 PM . Last Modified: ‎2024-03-19 11:44 PM

Back-UPS 650 boots to "sleep mode" after replacing battery. Functions as inverter, but not as UPS.

Hi All,

I replaced the battery in my Back-UPS 650 (Model #BK650MC).

Now when I power up the UPS it goes directly to sleep mode, beeping once every 4 seconds.

If I depress the rocker switch in the direction of the "no alarm" icon, the UPS turns on and supplies power perfectly. But it will not go "off battery" after that. I thought maybe for some reason it's not sensing the line voltage? So I tried this in several different outlets. I've tried it with the unit plugged in first, and with plugging the unit in after the battery is supplying power to the outlets. Neither way will kick the unit out of backup mode.

There are microswitches in the back, but a.) I don't think they got switched somehow and b.) I don't quite understand what they do (nor have I been able to find any documentation on them). Not sure if there's a possible fix there or not?

When I press "test" on the rocker switch (by rocking it away from the "no alarm" icon) nothing happens.

Does anybody know why this might happen?

Is it possible the unit somehow become damaged when the last battery died (doesn't seem likely)?

Again, it functions perfectly as an inverter. But not as a UPS, at the moment.

Any info/ideas/help greatly appreciated.

Thank you,

Bud

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 650
  • mode
  • sleep
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-11 10:58 PM . Last Modified: ‎2024-03-19 11:44 PM

0 Likes
0
2422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:58 PM . Last Modified: ‎2024-03-19 11:44 PM

Hi Jon,

Thank you for answering. It's an APC battery, but one with fewer amp-hours, which I don't think should be a concern. Also, the battery cirucuit appears to be working fine as the unit will operate as an inverter (just not as a UPS).

I replaced F3 today and it blows immediately upon plugging the unit in. 

I wonder if the fuse was placed there to protect the unit from a sticking relay? I ask because that's where the F3 fuse connects.

I'll have a closer look at things later.

I'll update here to help anybody who might have a similar issue in the future.

Thank you for your help,

Bud

See Answer In Context

  • Tags:
  • f3
  • fuse
  • relay
  • tranformer
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-07-11 10:58 PM . Last Modified: ‎2024-03-19 11:44 PM

0 Likes
0
2423
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:58 PM . Last Modified: ‎2024-03-19 11:44 PM

Hi Jon,

Thank you for your reply and for the manual that has the "option switch" settings listed in it. I traced things out in the order implied by your response. The main breaker was fine. The UPS is well-past warranty so I didn't mind opening it up to check the internal fuses. Indeed fuse F3--1A 125 volts--is reading infinity.

Any idea who the most likely downstream  culprit is that caused it to blow?

In the meantime I'll check my stash to see what I have for fuses. I believe I just came across some of these the other night.

Peace,

Bud

  • Tags:
  • 650
  • back-ups
  • fuse
  • mode
  • sleep
  • sleepmode
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-11 10:58 PM . Last Modified: ‎2024-03-19 11:44 PM

0 Likes
0
2423
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 10:58 PM . Last Modified: ‎2024-03-19 11:44 PM

Hi Jon,

Thank you for answering. It's an APC battery, but one with fewer amp-hours, which I don't think should be a concern. Also, the battery cirucuit appears to be working fine as the unit will operate as an inverter (just not as a UPS).

I replaced F3 today and it blows immediately upon plugging the unit in. 

I wonder if the fuse was placed there to protect the unit from a sticking relay? I ask because that's where the F3 fuse connects.

I'll have a closer look at things later.

I'll update here to help anybody who might have a similar issue in the future.

Thank you for your help,

Bud

  • Tags:
  • f3
  • fuse
  • relay
  • tranformer
Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore