Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Back UPS 650 MUS problems

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back UPS 650 MUS problems
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
154
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:05 AM . Last Modified: ‎2024-03-22 12:58 AM

0 Likes
5
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:05 AM . Last Modified: ‎2024-03-22 12:58 AM

Back UPS 650 MUS problems

Hello all. I was recently given the task of checking the status of our old UPS 650's.

The first thing I was told to do, by apc tech support, was to unplug all load connections. Then perform a battery charge, which took 8-10 hours. Once the charging was completed, I was told to plug a "small load" into the UPS and unplug the UPS from the wall outlet.

I did that and was told the battery should keep the small load powered. It did not power the fan(small load) for even 1 second. The UPS then emitted a steady tone until I either turned off the UPS or plugged it back into the wall.

Does this mean my battery is "toast"? Thank you in advance for your time and assistance.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:06 AM . Last Modified: ‎2024-03-22 12:58 AM

0 Likes
0
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:06 AM . Last Modified: ‎2024-03-22 12:58 AM

Hello all. I was recently given the task of checking the status of our old UPS 650's.

The first thing I was told to do, by apc tech support, was to unplug all load connections. Then perform a battery charge, which took 8-10 hours. Once the charging was completed, I was told to plug a "small load" into the UPS and unplug the UPS from the wall outlet.

I did that and was told the battery should keep the small load powered. It did not power the fan(small load) for even 1 second. The UPS then emitted a steady tone until I either turned off the UPS or plugged it back into the wall.

Does this mean my battery is "toast"? Thank you in advance for your time and assistance.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:05 AM . Last Modified: ‎2024-03-22 12:58 AM

0 Likes
0
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:05 AM . Last Modified: ‎2024-03-22 12:58 AM

Model # BK650MUS
Serial # BG024516432
I believe the unit is around 8 years.
The battery has never been replaced. At least, there is no record of it.

The LED indicators? There are none. There is a green light on the power switch on the front of machine. That is the only light anywhere on the machine. If I remove the load on the unit and then unplug it, I get a single beep every 5 seconds or so.

3-5 years? Yikes, I think I mgith just have a battery issue!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 04:05 AM . Last Modified: ‎2024-03-22 12:58 AM

0 Likes
0
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:05 AM . Last Modified: ‎2024-03-22 12:58 AM

Based from the serial number your unit was manufactured on the 45th week of 2002 and that makes it 8 years old already. The battery for this UPS is RBC4 and the single beep every 5 second indicates that the UPS is on battery. Unfortunately the one that you have cannot support the load anymore, it goes to overload when loads are attached.

Considering the age of your UPS, we can also suggest that you look into trading up your old unit and get the most updated UPS thru the APC TradeUPS program. It works like, you'll trade-in your old unit and we would give you the maximum VA capacity that you can purchase. On top of that, there is going to be a discount on the UPS that you've opted to buy and we'll take care with the disposal of your old one.

If you'd like to know more about APC TradeUPS please feel free to call our APC Support Team at 800.800.4272

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:05 AM . Last Modified: ‎2024-03-22 12:58 AM

0 Likes
0
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:05 AM . Last Modified: ‎2024-03-22 12:58 AM

Thank you for the response. I am familiar with the TradeUPS option. That seems like a good idea.

My employer would like to simply replace the dead battery. If you are saying the UPS itself cannot support that load does this mean a new battery would not help?

The single beep only occured when there was not load connected and the UPS was unplugged from wall outlet.

Also, the serial number tells you the year first, then the week? 0245 means '02, week 45? Thanks again. You have been extremely helpful.

Paul

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 04:05 AM . Last Modified: ‎2024-03-22 12:58 AM

0 Likes
0
1310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:05 AM . Last Modified: ‎2024-03-22 12:58 AM

I agree with Clarkson. If you are going to purchase APC batteries they are covered with 1 year warranty. If you opted for TradeUPS the next UPS of yours might have a 2 or 3 year warranty for both the UPS and the battery that came with it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:06 AM . Last Modified: ‎2024-03-22 12:58 AM

0 Likes
0
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:06 AM . Last Modified: ‎2024-03-22 12:58 AM

Hello all. I was recently given the task of checking the status of our old UPS 650's.

The first thing I was told to do, by apc tech support, was to unplug all load connections. Then perform a battery charge, which took 8-10 hours. Once the charging was completed, I was told to plug a "small load" into the UPS and unplug the UPS from the wall outlet.

I did that and was told the battery should keep the small load powered. It did not power the fan(small load) for even 1 second. The UPS then emitted a steady tone until I either turned off the UPS or plugged it back into the wall.

Does this mean my battery is "toast"? Thank you in advance for your time and assistance.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore