Back-UPS 500 - Alternative Replacement Battery

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS 500 - Alternative Replacement Battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
W400
W400
Cadet

Posted: ‎2025-09-18 10:27 AM . Last Modified: ‎2025-09-18 10:30 AM

0 Likes
5
731
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-18 10:27 AM . Last Modified: ‎2025-09-18 10:30 AM

Back-UPS 500 - Alternative Replacement Battery

Hello,

 

I have a 3-year old Back-UPS 500 (Model BX500CI). The battery is getting weak, and needs replacement.

 

According to the APC website, this model takes a APCRBC114 battery.

 

There is only one supplier where I live that has this battery. It is an official APC Replacement Battery, and costs as much as a replacement UPS.

 

Could a CSB HR1234WF2 Battery (12v 9.0Ah) be used instead?

 

Would it fit within the housing of the Back-UPS 500 (Model BX500CI)?

 

Dimensions of APCRBC114 (12v 6.4Ah)

H : 100mm

W : 53mm

D : 153mm

 

Dimensions of CSB HR1234WF2 Battery (12v 9.0Ah)

H : 94mm

W : 65mm

D : 151mm

 

 

Link to BX500CI

https://www.se.com/uk/en/product/BX500CI/apc-backups-500va-tower-230v-3x-iec-c13-outlets-avr/

 

Link to Replacement RBC 114 Battery

https://www.se.com/uk/en/product/APCRBC114/apc-replacement-battery-cartridge-114-with-2-year-warrant...

 

Attachments
Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Teken
Kirk Teken
Kirk

Posted: ‎2025-09-19 05:29 AM

0 Likes
0
728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-19 05:29 AM

Pretty much on any given day I would say yes this would be a simple drop in replacement.

 

But, you’ll need to measure the internal battery compartment to be sure for proper width spacing.

 

As the CSB cell is 65 mm vs 53 mm wide all other dimensions are fine. After reviewing the original battery specifications if true the unit was provided with a very low amp hour 12 VDC cell of 4.3 AH?!? 🤦‍♂️

 

If the CSB fits which you have a better than 50% chance it will after confirming internal spacing. That RBC will provide double the operational runtime vs the OEM! 🤟

 

Also normally I would call out the secondary installation steps but your unit appears to be a very simple basic unit with no communication port for APC Power Chute Software. ☹️

 

As such, once you install and connect the battery terminals to the RBC. Apply AC power to the unit without turning it on. Allow the cell to fully charge for at least 24 hours with nothing attached.

 

Once fully charged turn the unit on and allow the system to complete the self test and wait for the RBC to fully charge.

 

Next connect at least 30% or more load to the unit. Disconnect AC Mains and allow the system to run until it turns off.

 

Once complete restore AC Mains and allow the RBC to fully charge than turn the unit back on if it doesn’t turn on by itself automatically.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

W400
W400
Cadet

Posted: ‎2025-09-21 04:38 AM

0 Likes
1
677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-21 04:38 AM

Teken,

 

Thanks very much for your detailed reply.  I will measure the UPS sometime in the next few days, when I have more time.

 

When I bought the BX500CI about 3 years ago, I also purchased a BX750MI for a different computer.  I think it would be wise to also replace its battery (it uses the CSB HR1234WF2). 

 

The BX500CI doesn't have a usb interface for PowerChute, however the BX750MI does.

 

Should I follow the same steps you outlined in your reply when replacing the BX750MI battery?  Is there anything additional I need to do with PowerChute to re-calibrate the runtime, or otherwise let PowerChute know that the battery is new?

Reply

Link copied. Please paste this link to share this article on your social media post.

W400
W400
Cadet

Posted: ‎2025-09-21 06:36 AM

0 Likes
1
698
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-21 06:36 AM

Teken,

 

Thanks very much for your detailed reply.  I will measure the UPS sometime in the next few days, when I have more time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-09-22 04:53 AM

In response to W400
0 Likes
0
690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-22 04:53 AM

Please do follow up once you confirm as I’m sure the information will help the next person asking the same.

 

Upon confirmation please do mark the reply that answered your query as a solution to help others in the future. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-09-23 06:09 AM

In response to W400
0 Likes
0
674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-23 06:09 AM

BX750MI: Upon RBC replacement update the battery installation date via APC Power Chute if available. As doing so resets internal counters and adjust charging tables if applicable.

 

Allow the new RBC to recharge for 24 hours or when it shows 100% SOC (State of Charge).

 

Manually initiate a self test and let pass and allow the RBC to recharge back to 100% SOC. Complete the process by manually initiating a battery calibration if available via Power Chute Software with a minimum of 30% attached load or greater.

 

Allow the process to complete and allow the RBC to recharge back to 100% SOC. This procedure will teach the system the SOC / Health to better reflect the operational runtime on the LCD, Power Chute etc.

 

If there is no battery calibration available in Power Chute simply remove AC Mains from the system and allow it to shutdown by itself ensuring there is at least 30% or greater load.

 

In this specific case disconnect the USB cable from the computer system that runs Power Chute Software. 

You can use any resistive load like a heater, fan etc to achieve 30% or greater.

 

Final step is to simply use a sharpie or label printer to mark the RBC installation & battery calibration date on the cartridge.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore