Back-UPS 1500

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Back-UPS 1500
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
100
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
RichardH_apc
Crewman RichardH_apc
Crewman

Posted: ‎2021-06-28 05:38 AM . Last Modified: ‎2024-03-27 12:50 AM

0 Likes
5
1121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:38 AM . Last Modified: ‎2024-03-27 12:50 AM

Back-UPS 1500

Hi,

I'm an owner of a Back-UPS 1500 (home use). I've had this unit for approx. two years and it has worked flawlessly. I use this unit to provide back-up power to my home network equipment - network switches, servers and firewall. Also connected to this UPS, is a standard PDU bar. Attached to the mains lead for this PDU is an RCD plug with a "Test" button. Today, I accidentally hit this button which in turn tripped the main RCD to the house, instead of just tripping the RCD on the mains cable to the PDU. Along with this, the UPS switched to battery mode, which I'm a little concerned about. In theory, loss of power should switch the unit to battery, but in this case where there was possibly earth leakage after pressing the test button, should the UPS itself not have tripped?

I'm not an electrician so any advice I can get on this would be greatly appreciated.

One last note - I have recently moved all of my IT equipment to an 18u metal server rack (inc. the UPS with external battery). I'm concerned about grounding/earthing, where in the unfortunate event that there is a wiring fault and the cabinet itself becomes live, how would I link the cabinets earth lug to the UPS mains lead earth wire?

Thanks and regards,

Richard

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • earth
  • earthbonding
  • rcd
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:38 AM . Last Modified: ‎2024-03-27 12:50 AM

0 Likes
0
1121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:38 AM . Last Modified: ‎2024-03-27 12:50 AM

Yes, essentially it would be the same electrical point.

Secret Squirrel

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:38 AM . Last Modified: ‎2024-03-27 12:50 AM

0 Likes
0
1121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:38 AM . Last Modified: ‎2024-03-27 12:50 AM

Hi Richard,

I cant really speak for the RCD, as to why it may have tripped the main breaker. It would appear the Main Breaker observed something similar to a direct short. As for the UPS, it will certainly transfer to battery power once the RCD removes the electrical source, as it is designed to do so. Once the UPS switches to battery, it essentially electrically isolates itself from the electrical circuit. In theory, the unit can safely be removed from the electrical outlet and carried around while On-battery, without fear of electrical shock.

Schneider Electric does manufacture a Smart-UPS line of UPS which have EPO capabilities if this is something you are interested in having. The Back-UPS 1500 however, does not have this capability.

As for fears of properly grounding the 18U rack, you may connect a small ground wire between the rack and the center screw of your electrical wall plate where the UPS is plugged in. Although the UPS disables the Neutral/Hot blades during transfer to battery as to not back-feed, the ground reference is still actively connected.

If in doubt, I would suggest checking with your local electrical code for approved methods of grounding.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

RichardH_apc
Crewman RichardH_apc
Crewman

Posted: ‎2021-06-28 05:38 AM . Last Modified: ‎2024-03-27 12:50 AM

0 Likes
0
1121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:38 AM . Last Modified: ‎2024-03-27 12:50 AM

Hi,

Thanks for your very helpful response! In regards to grounding the rack, I live in the UK so there isn't an accessible earth connection on the face plates of the sockets. This may sound a little crazy, but I've got a three pin plug in which I've removed the live and neutral pins from, leaving just the earth, with an earth wire attached. I haven't actually used this, but in theory, if I attached the other end of this wire to the cabinets earth stud and then plugged the plug into a wall outlet - do you think this will provide ground to the cabinet?

Thanks again!

Regards,

Richard

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:38 AM . Last Modified: ‎2024-03-27 12:50 AM

0 Likes
0
1121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:38 AM . Last Modified: ‎2024-03-27 12:50 AM

Yes in theory this should provide the ground connection your looking for however of course, I must advise you you check with your local electrical code to ensure you meet the local requirements.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

RichardH_apc
Crewman RichardH_apc
Crewman

Posted: ‎2021-06-28 05:38 AM . Last Modified: ‎2024-03-27 12:50 AM

0 Likes
0
1121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:38 AM . Last Modified: ‎2024-03-27 12:50 AM

Perfect, thanks for that! I'll check that out also. In regards to the earth wire in the mains lead to the UPS, if I was to attach a standard PDU bar with an internal earth connection to the UPS, would connecting the earth stud on the PDU to the earth stud of the rack be the same as running an earth wire direct from the wall outlet? Would the earth connection from the mains lead to the PDU link to the earth wire of the mains lead to the UPS? Which in theory if it does, I can use the same earth connection as the UPS uses?

Thanks again,

Regards,

Richard

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:38 AM . Last Modified: ‎2024-03-27 12:50 AM

0 Likes
0
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:38 AM . Last Modified: ‎2024-03-27 12:50 AM

Yes, essentially it would be the same electrical point.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of