Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Back-UPS 1500 Preventing Computer Auto Start

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: Back-UPS 1500 Preventing Computer Auto Start
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
schmieg
schmieg
Explorer

Posted: ‎2024-12-30 10:10 AM . Last Modified: ‎2024-12-30 01:12 PM

0 Likes
6
1475
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-30 10:10 AM . Last Modified: ‎2024-12-30 01:12 PM

Back-UPS 1500 Preventing Computer Auto Start

My Back-UPS 1500 has been working flawlessly for a couple of years now, but, in the last three weeks, the computer cannot auto start at the prescribed time in the CMOS while connected to the UPS. It will work properly if plugged directly into the wall. The logs show no failures. Is this an indication of a problem with the UPS or should I be looking at a new Power supply in the computer or elsewhere? I would hate to stop using the UPS on a permanent basis, but it may become necessary for network operation.

 

The computer in question is a Dell XPS 8930 with Geforce 1000 video, Samsung 970 EVO Plus 1TB SSD, Samsung 870 QVO 4TB, and OEM Blue Ray Optical drive.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Teken
Champion

Posted: ‎2024-12-31 07:54 AM

0 Likes
0
1453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-31 07:54 AM

I’m not clear how you’re actually testing this system and how everything is connected so will offer some basic guidance.

 

Computer: Have nothing connected to the computer system. While the system is on and running remove AC Mains from the wall outlet.

 

Wait ten seconds and apply power to the system. Does the computer restart as expected?!? Is the date and time in the BIOS correct?!?

 

Once the computer boots up and you log into the system is the date and time correct?!?

 

If all the above is fine and passes this basic test. Proceed to connect the computer to the UPS (Without the USB cable).

 

Remove AC Mains from the wall that powers the UPS. Let it run and shutdown by itself.

 

Apply power back to the UPS and let it recharge the cells to 100%. If the UPS turns back on or if you need to press the power button to the UPS do so.

 

Does the computer restart as before in the first test?!?

 

Let me know the results of both tests. 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Teken
Teken
Champion

Posted: ‎2024-12-31 07:54 AM

0 Likes
0
1454
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-31 07:54 AM

I’m not clear how you’re actually testing this system and how everything is connected so will offer some basic guidance.

 

Computer: Have nothing connected to the computer system. While the system is on and running remove AC Mains from the wall outlet.

 

Wait ten seconds and apply power to the system. Does the computer restart as expected?!? Is the date and time in the BIOS correct?!?

 

Once the computer boots up and you log into the system is the date and time correct?!?

 

If all the above is fine and passes this basic test. Proceed to connect the computer to the UPS (Without the USB cable).

 

Remove AC Mains from the wall that powers the UPS. Let it run and shutdown by itself.

 

Apply power back to the UPS and let it recharge the cells to 100%. If the UPS turns back on or if you need to press the power button to the UPS do so.

 

Does the computer restart as before in the first test?!?

 

Let me know the results of both tests. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

schmieg
schmieg
Explorer

Posted: ‎2024-12-31 10:27 AM

0 Likes
4
1434
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-31 10:27 AM

I think I have solved the problem and I don't now think it is the UPS. The computer had been working when I plugged it into the wall outlet, but it failed to boot this morning.  I had to push the BIST button on the power supply for several minutes to get it up and running, so I am 95% sure, at this time, that the power supply in the computer is failing.

 

Regarding your tests, yes, everything worked previously as I had performed those as you set forth. The only failure was the automatic boot at the set time. I am now setting up the system to run continuously until a new power supply arrives in two days. Thank you for your response. I was thinking that the power supply was the problem until I found that the computer would boot at the set time from the wall socket, but now I think the UPS is working properly and it's just that the power supply failure to boot was intermittent. If the problem is still there after a new power supply, I will re-evaluate, but I really don't expect that to happen based on what happened today.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-01-02 03:31 AM

In response to schmieg
0 Likes
3
1426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-02 03:31 AM

Great to hear and do follow up as to the final outcome. 

Happy New Years! 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

schmieg
schmieg
Explorer

Posted: ‎2025-01-04 07:19 PM

In response to Teken
0 Likes
0
1381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-04 07:19 PM

Will do as soon as things are up and running again and I can test it fully.

Reply

Link copied. Please paste this link to share this article on your social media post.

schmieg
schmieg
Explorer

Posted: ‎2025-01-08 10:55 AM

In response to Teken
0 Likes
1
1347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-08 10:55 AM

I replaced the computer in question after it failed to even power on with the new power supply. Everything is working fine now with the new computer. I suspect the old power supply was going bad and damaged something on the motherboard, but it was going bad slowly and intermittently. The UPS connection failure and the wall socket connection success caused me to think that the UPS was the problem, but then the subsequent wall socket connection failure made me rethink the issue.

 

I am sorry for causing any concern on your part, but thrilled that things are working again absent the expense of a new computer <grin>. Thank you for your help. I have been using your products for many years now and plan to continue doing so.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2025-01-09 04:17 AM

In response to schmieg
0 Likes
0
1333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-09 04:17 AM

Appreciate the follow up and the final outcome.

 

Rock On . . . 🤟

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore