BX1500LCD Zero Runtime

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BX1500LCD Zero Runtime
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Janeway Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

0 Likes
6
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

BX1500LCD Zero Runtime

I bought my BX1500LCD in June of 2010. It's used to support a linux home server with accessories and is controlled by an apcuspd daemon. In August of this year, after around 14 months of normal operation, the unit suddenly started to give indications of low battery at 100% charge with a short available run time. I got the same indications through both the software interface and on the front panel of the unit: 100% charge with only a short (or even zero) run time available. I didn't expect the battery to have reached end-of-life after only 14 months but that's what it seemed to be, so I ordered a new battery pack from APC.

When the new battery pack arrived, I put it in and let it charge for a day but even so, I was still getting the same indication. I both Googled and checked the APC Knowledge Base, where I found something called a Manual Battery Calibration procedure, which I performed. I shut down the computer attached to the UPS, loaded it up to 75% load with pedestal fans and incandescent lamps, and then pulled the plug. It ran for about five minutes before shutting down. I removed the fans and lights and plugged the unit in and let it charge up again. Unfortunately, the UPS is still indicating 100% charge with zero available run time.

In its present condition, the server attached to the UPS will shut down immediately if there is a power outage due to the low battery indication. At least it's a clean shutdown but still, that's not the way it's supposed to work.

At this point, I really don't know what to do. Should I RMA the UPS under warranty? Or are there additional troubleshooting steps I could perform? Any advice or suggestions would be appreciated.

Thanks!

Bill

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

0 Likes
0
999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

Hmmm, the instructions on the APC website said 'at least 40%', IIRC. Anyway, I repeated the manual run time calibration. I shutdown the server and disconnected the USB cable from the UPS. I then loaded the unit up to 42% of rated load as indicated on the LCD panel and then I pulled the plug. The unit ran for 12:20 (mm:ss) before shutting down. I then plugged the unit back in, leaving the server off. There were still some minor loads on the unit ~ 20 watts. I let the unit charge to 100%, which took a little over two hours, before plugging in the USB cable and turning the server back on.

The unit LCD panel now indicates 100% charge, 7% load, and 1 minute of available run time.

Regrettably, I don't think that the manual run time calibration procedure is sufficient to fix my problem.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

0 Likes
0
999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

Bump. Any resolution ?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

0 Likes
0
999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

The old battery was probable fine all you need to do is preform a runtime calberation you can do that by putting on a non critical load such as a 100 watt light and pull the plug and let it run untill it shuts off

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

0 Likes
0
999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

As described in my initial post, I tried that, based on instructions on the APC website, but it did not help or affect the situation in any way.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

0 Likes
0
999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

It didn't work because the Load was to large to calibrate the load needs to be 30%

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

0 Likes
0
999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

i have a question - now after your calibration that you performed, when it says 100% battery charge and zero runtime, this is with the data cable attached. if you remove the USB data cable from your computer and UPS and put the UPS on battery, does it still shutdown immediately? i ask because i am wondering if something did happen and the unit requires a calibration, perhaps with a smaller load. without software intervention, it sounds like the UPS will run for the correct amount of time but because its confused, it tells the software you shutdown immediately.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

0 Likes
0
1000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-21 05:05 AM

Hmmm, the instructions on the APC website said 'at least 40%', IIRC. Anyway, I repeated the manual run time calibration. I shutdown the server and disconnected the USB cable from the UPS. I then loaded the unit up to 42% of rated load as indicated on the LCD panel and then I pulled the plug. The unit ran for 12:20 (mm:ss) before shutting down. I then plugged the unit back in, leaving the server off. There were still some minor loads on the unit ~ 20 watts. I let the unit charge to 100%, which took a little over two hours, before plugging in the USB cable and turning the server back on.

The unit LCD panel now indicates 100% charge, 7% load, and 1 minute of available run time.

Regrettably, I don't think that the manual run time calibration procedure is sufficient to fix my problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of