BX1500G - battery light blinking... but...

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
5
291

BX1500G - battery light blinking... but...

This question was originally posted by Taner on APC forums on 6/29/2013


Hello!

I have a BX1500G from Jan 2010 (still on original battery, front label is inscribed "Back-UPS XS 1500"), and when the battery light started blinking (and it's not carrying any load when unplugged from the wall), I initially suspected that I need a new battery.

Well, I decided to at least test the battery w/ my voltmeter, and it reads 21VDC.  I'm not sure what the nominal voltage is, to compare.

In case it matters, this UPS had been sitting around (unused) for maybe 6-8mo, and it had previously been working just fine.

Is this just a dead battery?  Should I simply order a new one?

Or are there any other steps I should take to ensure that's the issue at hand?

Thanks!

-Taner

Tags (2)

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
291

Re: BX1500G - battery light blinking... but...

This reply was originally posted by Angela on APC forums on 7/1/2013


Anytime a UPS sits unused, the battery should be disconnected or you can leave it plugged in and off to trickle charge the battery. A flashing battery icon indicates the battery is disconnected (or the UPS cannot see it cause the voltage is indeed too low).

I believe this UPS has a 24vDC battery bus so it should have a float voltage at about 27vDC.

How long have you left the UPS plugged in (either on or off) and charging to see if the blinking battery goes away? I'd give it at least 24 hours if you can and if no change, I agree with a battery replacement.

See Answer In Context

BillP
Administrator Administrator
Administrator
0 Likes
0
291

Re: BX1500G - battery light blinking... but...

This reply was originally posted by Taner on APC forums on 7/1/2013


Hi Angela,

Thanks for the response!  Yeah, normally I'd disconnect the battery if I had expected to leave the UPS sitting for a while -- but we had moved homes and I forgot about the UPS, as I hadn't found an immediate use for it, so... yeah... it sat for a while 😕

Anyway, I'll leave it plugged in for a day or so -- I hadn't done that yet, since I initially thought the flashing battery icon meant the battery was *dead* (as in, needing to be replaced), and not that it might just be low on charge 🙂

I'll report back in ~24hours or so 🙂

-Taner

See Answer In Context

5 Replies 5
BillP
Administrator Administrator
Administrator
0 Likes
0
292

Re: BX1500G - battery light blinking... but...

This reply was originally posted by Angela on APC forums on 7/1/2013


Anytime a UPS sits unused, the battery should be disconnected or you can leave it plugged in and off to trickle charge the battery. A flashing battery icon indicates the battery is disconnected (or the UPS cannot see it cause the voltage is indeed too low).

I believe this UPS has a 24vDC battery bus so it should have a float voltage at about 27vDC.

How long have you left the UPS plugged in (either on or off) and charging to see if the blinking battery goes away? I'd give it at least 24 hours if you can and if no change, I agree with a battery replacement.

BillP
Administrator Administrator
Administrator
0 Likes
0
292

Re: BX1500G - battery light blinking... but...

This reply was originally posted by Taner on APC forums on 7/1/2013


Hi Angela,

Thanks for the response!  Yeah, normally I'd disconnect the battery if I had expected to leave the UPS sitting for a while -- but we had moved homes and I forgot about the UPS, as I hadn't found an immediate use for it, so... yeah... it sat for a while 😕

Anyway, I'll leave it plugged in for a day or so -- I hadn't done that yet, since I initially thought the flashing battery icon meant the battery was *dead* (as in, needing to be replaced), and not that it might just be low on charge 🙂

I'll report back in ~24hours or so 🙂

-Taner

BillP
Administrator Administrator
Administrator
0 Likes
0
291

Re: BX1500G - battery light blinking... but...

This reply was originally posted by Angela on APC forums on 7/1/2013


Alrighty. smile

BillP
Administrator Administrator
Administrator
0 Likes
0
291

Re: BX1500G - battery light blinking... but...

This reply was originally posted by Taner on APC forums on 7/3/2013


Quick follow-up...

After leaving the UPS plugged in overnight, it seems to be fine smile

Battery showing full, and I can unplug it from the wall and it carries load without an issue!

I guess I should have tested that before jumping to conclusions about the battery being actually dead....

Thanks!

-Taner

BillP
Administrator Administrator
Administrator
0 Likes
0
291

Re: BX1500G - battery light blinking...  but...

This reply was originally posted by Angela on APC forums on 7/3/2013


You're welcome.