Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84865members
354358posts

BX1300LCD and BX1500LCD - Same battery capacity? Run-time is same?

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
dustoffxl_apc
Cadet
0 Likes
2
162

BX1300LCD and BX1500LCD - Same battery capacity? Run-time is same?

This was originally posted on APC forums on 1/27/2008


I recently bought a BX1300LCD (1300VA). I was going to exchange it for the BX1500LCD, but it appears that the battery capacity is the same. If you compare the half-load and full-load, it appears the run-times would be the same, if under the same load.

Is it true that BX1500LCD uses same capacity battery?


BX1300LCD
Typical Backup Time
Half Load 18.4 minutes (390 Watts)
Full Load 6.4 minutes (780 Watts)

BX1500LCD
Typical Backup Time
Half Load 16.0 minutes (432.5 Watts)
Full Load 5.3 minutes (865 Watts)


Accepted Solutions
KVAr_apc
Captain
Captain
0 Likes
0
162

Re: BX1300LCD and BX1500LCD - Same battery capacity? Run-time is same?

This was originally posted on APC forums on 1/28/2008


dustoffxl wrote:
I recently bought a BX1300LCD (1300VA). I was going to exchange it for the BX1500LCD, but it appears that the battery capacity is the same. If you compare the half-load and full-load, it appears the run-times would be the same, if under the same load.

Is it true that BX1500LCD uses same capacity battery?


BX1300LCD
Typical Backup Time
Half Load 18.4 minutes (390 Watts)
Full Load 6.4 minutes (780 Watts)

BX1500LCD
Typical Backup Time
Half Load 16.0 minutes (432.5 Watts)
Full Load 5.3 minutes (865 Watts)
They're likely the same if the weight of the two units are very similar. I'm guessing a pair of 12v 9Ah. These are harder to find and you'd probably end up having to get OEM replacement if you want the same runtime as aftermarket look-a-like are likely to be 7.2Ah.

See Answer In Context

2 Replies 2
TheNotoriousKMP_apc
Sisko
Sisko
0 Likes
0
162

Re: BX1300LCD and BX1500LCD - Same battery capacity? Run-time is same?

This was originally posted on APC forums on 1/28/2008


As the batteries are still prototypes, I can only comment based on what I knew of the BX 1200 and 1500 prior to the LCD series. Both used the same batteries, so the ~40W difference in capacity based on loads seems accurate for the runtime. Just because it's 200VA, does not mean it is also 200W.

KVAr_apc
Captain
Captain
0 Likes
0
163

Re: BX1300LCD and BX1500LCD - Same battery capacity? Run-time is same?

This was originally posted on APC forums on 1/28/2008


dustoffxl wrote:
I recently bought a BX1300LCD (1300VA). I was going to exchange it for the BX1500LCD, but it appears that the battery capacity is the same. If you compare the half-load and full-load, it appears the run-times would be the same, if under the same load.

Is it true that BX1500LCD uses same capacity battery?


BX1300LCD
Typical Backup Time
Half Load 18.4 minutes (390 Watts)
Full Load 6.4 minutes (780 Watts)

BX1500LCD
Typical Backup Time
Half Load 16.0 minutes (432.5 Watts)
Full Load 5.3 minutes (865 Watts)