BX1000G discharged, won't charge, PowerChute cannot detect?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BX1000G discharged, won't charge, PowerChute cannot detect?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:57 AM

0 Likes
1
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:57 AM

BX1000G discharged, won't charge, PowerChute cannot detect?

So I recently got a new UPS and hooked everything up 2 days ago.  Yesterday after seeing the charge still holding and full, I ran it on the battery for a few minutes to ensure that was working and went back to wall power.  This morning I was woken to it beeping and having for some reason completely discharged.

The only things attached to it were my PC and monitors, both of which were off (though my PC does still pull some wattage even while off, so I can charge my phone and such when attached to it).  We didn't have any sort of power outage (alarm clock attached to the other outlet on same circuit).  I have no idea what could or would have caused the unit to drain, and after installing the PowerChute software to hopefully answer that question I was left with another.

I'm currently running Win7 Home and after connecting the UPS, Windows automatically detected it as an APC USP.  PowerChute however lists it as an "unknown UPS model" and says the Device Communications cannot be established.  I'm at a loss of what to do and search engines have yielded me very outdated, or unusable information.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:56 AM

0 Likes
0
850
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:56 AM

if it were me, i'd start by rebooting/resetting the UPS to address the powerchute problem. since Windows detected it, we know it is plugged into the right port on both the UPS end and obviously on your computer USB port.

So, to reboot/reset the UPS, i'd turn off and remove your computer and anything else attached to the UPS. Turn the UPS off. Then unplug the UPS from the wall. You'll next need to disconnect the battery on the UPS and hold down the off button on the UPS for 10-15 seconds while the battery is disconnected.

Once that's complete, reconnect the battery, plug the UPS back in, and turn it on. Then i'd reconnect your computer and the USB cable and repeat and see if any change. If no change with PowerChute, also verify the UPS is still listed under Batteries in Windows at this time.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:56 AM

0 Likes
0
851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:56 AM

if it were me, i'd start by rebooting/resetting the UPS to address the powerchute problem. since Windows detected it, we know it is plugged into the right port on both the UPS end and obviously on your computer USB port.

So, to reboot/reset the UPS, i'd turn off and remove your computer and anything else attached to the UPS. Turn the UPS off. Then unplug the UPS from the wall. You'll next need to disconnect the battery on the UPS and hold down the off button on the UPS for 10-15 seconds while the battery is disconnected.

Once that's complete, reconnect the battery, plug the UPS back in, and turn it on. Then i'd reconnect your computer and the USB cable and repeat and see if any change. If no change with PowerChute, also verify the UPS is still listed under Batteries in Windows at this time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore