BX1000G 2 beeps every 2 seconds

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BX1000G 2 beeps every 2 seconds
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
121
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
14
3644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

BX1000G 2 beeps every 2 seconds

I purchased a BX1000G at Best Buy on 12/11/2010 and this evening (12/14/2010) I went down into my office the UPS was beeping twice about every 2 seconds. The UPS was connected to the wall with no load. I unplugged the UPS and it was aware it was unplugged. I plugged the UPS back into the wall and turned on my Mac mini. I unplugged the UPS from wall and my Mac mini immediately went off. I plugged the UPS back into the wall, looked at the battery level, and it was at 2 bars. I proceeded to unplug the UPS and reseat the battery, etc. Now, the UPS showed 0 bars. I don't understand this behavior at all. The UPS was plugged into the wall and the Mac mini was turned off for about 24 hours and in that time the UPS drained its battery without any load.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • battery
  • beeping
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
0
3643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

Hello.

I have the exact same issue. Brand new 1000 xs unit. Plug into wall and beeps twice every 2 seconds. No load at all. Nothing plugged in. What was the solution or issue?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
0
3643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

Have you properly connected the battery?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 14
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
0
3643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

I purchased a BX1000G at Best Buy on 12/11/2010 and this evening (12/14/2010) I went down into my office the UPS was beeping twice about every 2 seconds. The UPS was connected to the wall with no load. I unplugged the UPS and it was aware it was unplugged. I plugged the UPS back into the wall and turned on my Mac mini. I unplugged the UPS from wall and my Mac mini immediately went off. I plugged the UPS back into the wall, looked at the battery level, and it was at 2 bars. I proceeded to unplug the UPS and reseat the battery, etc. Now, the UPS showed 0 bars. I don't understand this behavior at all. The UPS was plugged into the wall and the Mac mini was turned off for about 24 hours and in that time the UPS drained its battery without any load.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
0
3644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

Pretty much the same problem as the OP. I have used lots of APC products so was kind of surprised to read about all the problems with this unit.

New unit, brought it home and set it up, ran through the configs, did an initial self test, everything looked great. Within 48 hours the unit was chirping at me every few seconds. Logged in and the PowerChute software popped up and told me there was an internal error. Tried to run the self-test and it failed, again with an internal error. BTW, it would not even try to go into self-test with the alarm silenced. Power cycled the unit and the alarm came right back. Turned the unit off for several hours and when it was turned back on the chirping had stopped, but the battery had gone from 100% to about 17% whiled turned off and I had no devices plugged in to the unit. A quick self-test took the unit to almost 0%. The battery has now been charging back up for several hours and is almost back to 100%. We'll see if it starts chirping again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
0
3644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

Hello.

I have the exact same issue. Brand new 1000 xs unit. Plug into wall and beeps twice every 2 seconds. No load at all. Nothing plugged in. What was the solution or issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
0
3644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

Have you properly connected the battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
0
3644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

id like to dust of this thread.

i purchased several of these units. some from office depot and thats where this one was from.

purchased it on wednesday of this week.

this morning it was doing the EXACT same behavior as the OP of this thread.. to the letter! beeps, but was showing online and knew it was on the utility power.i muted the speaker, however it kept discharging. i had items plugged up to it then entire time. i plugged up the laptop and it showed no faults however it could not complete a self test.. just stated it could not do it at this time..

then, after i plugged up the usb datacable, the unit started charging! so as i was doing the steps above (attempting self test...etc) the unit seemed to start charging. because i went into the tech screen and it showed "charging..."....

anyway, i traded two of these in (including this one) for the next size up, the 1300G model... will see how that works...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
0
3645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

Alan,

Aside from the chirping sound that is produce and an empty battery bar, do you also see the battery bar flashing?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
0
3644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

No, nothing was flashing, just an empty battery bar and no error codes of any kind. It was really weird that it discharged itself with no load and it was aware of the voltage from the wall. The indicators did not show that it was running on battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
0
3644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

I sent a PM to you Alan. Please feel free to respond back.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
0
3644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:54 AM . Last Modified: ‎2024-03-22 12:22 AM

You need to call apc there was a bad batch of bx1000g s
That went out and it looks like your charging systyrm failed and your unit will need replacing

Apc support 1-800-555-2725

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
0
3644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-22 12:22 AM

Breathing life back into an old thread...

Mine started chirping like this sometime last night. It's a replacement I've had for two days, direct from APC- a replacement for one that died from the F06 error (switching relay? problem).

Not exactly confidence inspiring.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
0
3645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-22 12:22 AM

Same here. Bought a BX100G in November of 2011. Experienced the same chirp-chirp; pause phenomenon as described.

Engaged tech support via chat (helpful but slightly tedious). Got an RMA (had to complain to get the pre-paid shipping). New unit arrived promptly.

Plugged it in (no equipment attached) and, within 2 days... chirp-chirp; pause. AND the on/off button wouldn't switch the unit off.

It also went to battery during a sag (<115 V) (still nothing plugged into it)... beeped... and the battery showed 40% charge.

No resolution; but useful to note that there WAS in fact, a manufacturing issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-22 12:22 AM

0 Likes
0
3645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-22 12:22 AM

I am having a similar problem with the same type of unit. I first bought one (no. 1) in December of 2010. I took it home and attempted to install it. The moment I first tried to activate it I received error messages. The "internal fault" warning came on. I called APC and they told me to that the unit was defective. I took it back to the retailer and received a replacement (no 2).

The replacement died the afternoon of July 25, 2012, just as I was about to leave town for an 8 day vacation. The computer was going to be used by my house sitter. APC phone support talked me through some diagnostics, then told me that the unit had failed. Since it was still under warranty they would send me a replacement, but I would be responsible for the cost of shipping the failed unit (no. 2) back to them.

The replacement unit (no. 3) arrived while I was out of town. When I returned I attempted to install it. The unit started beeping 4 times every 30 seconds. I found that the surge suppressed outlets worked fine. However, I found that the unit was running on battery power even though it was plugged in and receiving power from the utilities. Power out was 114 V. Power in was 0 V.

So, here I am with 2 faulty units and the expectation of having to pay to send both of them back to APC. I have not yet talked with customer service about this latest failure, but I am tempted to give up and buy a unit from a different manufacturer. Rather than pay to send the units back to APC, I may just recycle both batteries and enclosures and tell APC that they have lost my business.

Reply

Link copied. Please paste this link to share this article on your social media post.

SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-22 12:21 AM

0 Likes
1
3645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:55 AM . Last Modified: ‎2024-03-22 12:21 AM

Time to bump this back up again.  I have a Backups Pro 700 that has been in operation for a few years now (may still be in warranty), and this morning around 3:30a cst I did notice some extra bright lightning flashes (since my eyes were closed) and heard all the ups units in the house beep in unison as the power must have flickered once or twice.

This morning this unit was behaving exactly like the OP's--beeping 2x every second, and flashing blank battery bar.  Any ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

COTR
COTR
Cadet

Posted: ‎2025-01-04 10:19 AM

In response to SamirD_apc
0 Likes
0
1163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-04 10:19 AM

I have BN1500M2-CA at the non profit and it is beeping 2 beeps every few seconds and Empty battery symbol is flashing,
the property caretaker just mutes it without thinking why, What is the reason, I am afraid if I buy a new battery that will be wasted if the UPS is defective. Please guide

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore