BR800 - after green self test, chrips in an irregular pattern continuously

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BR800 - after green self test, chrips in an irregular pattern continuously
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

0 Likes
9
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

BR800 - after green self test, chrips in an irregular pattern continuously

Hello,

I have two Back-UPS RS 800 units in service for approximately 4 years.

One of them started chirping every few hours, it seemed, then every hour, then it got closer together. I assumed it had failed a test so I shut the unit down and restarted it. The battery diagnostic IMMEDIATELY failed and went red.

So I ordered a battery and replaced it.

Here is where I am confused -- I let the battery charge overnight, I turn the unit on, and the diagnostic succeeds. Green light.

The unit then proceeds in an irregular pattern (once every few seconds, then maybe not for 8 minutes, then every 2 minutes, etcetera) to quickfly flip on and off battery and chirp once.

There is no power fluctuation that I know of in the room -- which has another Back UPS RS 800 which is not complaining. I tried swapping the two units to see if maybe the outlet was providing bad power, but the symptoms remained (one fine, one not).

Any ideas?

thank you for your time!

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • backups
  • beep
  • br800
  • chirp
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

0 Likes
0
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

no, it will be fine. i mean sensitivity just affects how sensitive the UPS is to electrical noise, etc rather than letting it pass through to your computer.

an average computer would be fine on low sensitivity in my opinion. i just wanted you to adjust it to see if that was the issue so you dont have to do that with the computer connected.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

0 Likes
0
1783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

hmm definitely sounds strange.

try doing the following:

1 Disconnect any attached load.
2 Unplug the UPS from the wall socket.
3 Disconnect the UPS' internal battery.
4 Push and hold the "On" button on the UPS for 5 seconds
5 Reconnect internal battery.
6. Plug UPS in to known good power source.
7: Turn UPS on.

let us know if it still does the same thing after doing the steps above.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

0 Likes
0
1783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

Hello,

It still does the same thing. If anything it's doing it more rapidly? Could just be random chance. Powered on it almost continually cycles, chirping once each time.

Without power (AC or battery) holding the button had no noticeable effect.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

0 Likes
0
1783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

ok so you are positive it is the amber ON BATTERY LED - meaning the UPS is possibly cycling between online and on battery?

chirping usually happens in conjunction with the replace battery LED so I just want to be sure. replace battery is the fourth LED down on the front panel if its hard to see.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

0 Likes
0
1783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

Absolutely -- it is cycling from the top and second most top lights, the short beep (or chirp) occurs when it's coming back from the on battery light to the power light -- I think, it's rather quick. I hear it accessing the battery -- that sort of mechanical click sound. It's very brief.

After I posted that last message I left it on for awhile, the chirps became less continuous. When it first powered on, flip, flip, flip, flip, then it went for a few minutes, then flip, then a minute, then flip, flip, then it was like 10 minutes, flip.

each flip had a chirp 😞

This morning I tried replacing the original battery just for giggles as I had not sent it off yet. It behaved the same, except after a few minutes when I held power for a test it failed the battery and lit replace. So I put the new battery back in. Still chirping. πŸ˜›

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

0 Likes
0
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

Would low sensitivity enable it to still provide backup power for , say, a computer setup? Manual implied that low sensitivity was bad for this.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

0 Likes
0
1785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

no, it will be fine. i mean sensitivity just affects how sensitive the UPS is to electrical noise, etc rather than letting it pass through to your computer.

an average computer would be fine on low sensitivity in my opinion. i just wanted you to adjust it to see if that was the issue so you dont have to do that with the computer connected.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

0 Likes
0
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

no problem. but if it starts clicking again, then that must mean you are starting to have an electrical noise issue that needs to be looked at in your location. glad to be of help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

0 Likes
0
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

Happy to report that setting sensitivity to "low" has apparently resolved the issue -- and still seemed to provide power to the system. πŸ™‚

Other unit is still on medium, or factory default.

Thank you for your time !!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

0 Likes
0
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 12:54 AM . Last Modified: β€Ž2024-03-22 03:50 AM

yeah i am not sure what is causing it. as long as the sensitivity is set to low, thats all i got 😞

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore