Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

BR1500I overload led blink - internal fault

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BR1500I overload led blink - internal fault
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:10 AM . Last Modified: ‎2024-03-21 05:04 AM

0 Likes
13
1695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:10 AM . Last Modified: ‎2024-03-21 05:04 AM

BR1500I overload led blink - internal fault

Hi, I connected 2 power strip with a switch to my ups.
A power strip power router and PC. The other power monitors and various accessories.
Sometimes the UPS goes into alarm when I turn the power strip on, but after a few seconds resumes normal operation.
This night, however, has triggered the breaker went out the electrical system and all equipment. From that moment marks the UPS overload remains constant even unplugging everything except the main power cable. Disconnecting the battery rightly points out that it is not present but reports linking it back overhead.
This type of problem seems common and I would like to know which component is replaced (or other relay or MOSFET).
I opened the ups and there are no signs of burning.
How can I fix it?
Thank you.
p.s. I am Italian and use google translate.

Message was edited by: Master of Mouse

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

0 Likes
0
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

I think too. For this I buy a SMT1500I 🙂

Message was edited by: Master of Mouse

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:10 AM . Last Modified: ‎2024-03-21 05:04 AM

0 Likes
0
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:10 AM . Last Modified: ‎2024-03-21 05:04 AM

The fan work fine. Even the 3 relays work well. Remain the MOSFET and any SMD components.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:10 AM . Last Modified: ‎2024-03-21 05:03 AM

0 Likes
0
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:10 AM . Last Modified: ‎2024-03-21 05:03 AM

It Could Be A Fan Fault

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:10 AM . Last Modified: ‎2024-03-21 05:03 AM

0 Likes
0
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:10 AM . Last Modified: ‎2024-03-21 05:03 AM

Ya I Don't Know For Sure But The Overload Flashing Could Be That The Ups Was Permanently Damaged From An Overload 😞
Is The Transformer Ok??
Otherwise We See A Lot Of Fan Faults That Cause The Overload Light To Blink

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

0 Likes
0
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

Fan and Transformer are ok
Even turning on all the equipment consumption does not exceed 400W
There may be peaks when active sockets of three monitors / PS3 / audio / accessories but they last less than a second.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

0 Likes
0
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

Hook It Up To Powerchute And See What It Has To Say

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

0 Likes
0
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

Warning overloaded. Load 0. Autonomy about 700 minutes.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

0 Likes
0
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

well if it says its overloaded at 0 watts the firmware seems to be corrupt

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

0 Likes
0
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

how can I fix it?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

0 Likes
0
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

Hi Master,

Aside from the Overload LED flashing, any other LED that is lit up?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

0 Likes
0
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

I Dont Know If You Can You Would Have To Reprogram It

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

0 Likes
0
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

no

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

0 Likes
0
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

Looks like your UPS can no longer be repaired.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

0 Likes
0
1695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:11 AM . Last Modified: ‎2024-03-21 05:03 AM

I think too. For this I buy a SMT1500I 🙂

Message was edited by: Master of Mouse

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore