BR1500GI Surge-only ports rating

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BR1500GI Surge-only ports rating
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
124
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:54 AM . Last Modified: ‎2024-03-21 04:34 AM

0 Likes
12
1958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:54 AM . Last Modified: ‎2024-03-21 04:34 AM

BR1500GI Surge-only ports rating

Why isn't there any "rating" (voltage and amperage) printed in the back of my BR1500GI (near the outlets)? I only see 230V 10A in the Input port of the UPS. With lower-end APC UPS (colored white) in our office, I see there are three ratings, one for the input port, one for the battery outlet ports, and one for the surge-only outlet ports. Now I'm wondering how much load is the limit of surge-only outlet ports and battery-backup outlet ports?

Please advise.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:33 AM

0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:33 AM

BUMP!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

BUMP!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

We don't have an rating for each individual outlet. We have a 10amp circuit breaker on the output and typically the power cords used are rated for 10amps as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

Ok. So basically, I should never increase 10A combined current draw on ALL the loads that are connected to the UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

Bump!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

..

Message was edited by: barryware

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

Barryware, why did you delete your message?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

Because.. I linked you to the spec sheet that states surge protection of the outlets (in joules).. After re-reading your post, I think you are more interested in capacity in amps / watts. I could not find a way to completely delete my post.

A simple solution would be to look at the reset / circuit breaker for the line in. All the outlets combined capacity would be equil to the capacity of the line in circuit breaker.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:34 AM

You are correct, I am interested with the voltage and current capacity of the surge only outlet ports.

What do you mean? Where do I get that line in information?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:33 AM

0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:33 AM

But why do older APC UPS (white-colored units) have 2 general rating, 1 for the battery backup outlets and 1 for the surge-only protected outlets?

That 10amp circuit breaker you mentioned, is it for the battery backup outlets (collective), for the surge-only protected outlets (collective), or for all outlets combined? The input port has a 230V 10A input rating though.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:33 AM

0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:33 AM

the breaker is for all the outlets. It's not specific to any one outlet or group of outlets. I'm not sure why the ratings on the units themselves have changed. I haven't personally seen that on any of the older units I've looked ast.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:33 AM

0 Likes
0
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:33 AM

By the way, here is one good example of the individual group ratings I am mentioning:

http://www.google.com/imgres?q=apc+ups+back+view&um=1&hl=en&client=firefox-a&rls=org.mozilla:en-US:o...

You can see that there are different current ratings for the surge-only port and battery-backup outlet ports.

Message was edited by: kevindd992002

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:33 AM

0 Likes
0
1958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:55 AM . Last Modified: ‎2024-03-21 04:33 AM

BUMP!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore