Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

BK650I: Use UPS only for correct shutdown/startup of Windows 7

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BK650I: Use UPS only for correct shutdown/startup of Windows 7
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:45 AM . Last Modified: ‎2024-03-22 01:14 AM

0 Likes
5
1178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:45 AM . Last Modified: ‎2024-03-22 01:14 AM

BK650I: Use UPS only for correct shutdown/startup of Windows 7

Hello,

I have installed a APC xxx UPS inline with a PC and want to reach the following functionality;

When power swichtes on, PC should boot and run, if power fails PC should shut down immediately. When power switches on again the PC should boot up.

Through the PowerChute software I was able to have the PC shutdown (hibernation switched off in Win7). The minimum time for this seems to be a minute. Is it possible to reduce this to 'immediate' or x seconds?

When the PC switches off, a dialog is offered. Users are able to abort the shutdown, Can I disable this?

When the power is back, the PC should boot again. Before (without UPS) we reached this by setting the option 'Boot After power failure' in the Intel Bios to [power on]. Unfortunatly with the UPS installed, when it switches off the PC, the power is not taken away from the outlet. Hence the motherboard does not sense that the power has been away and does not reboot after the power has been put back to the UPS. Is there a known workaround for this?


My current system configuration:
APC BK650I
Motherboard Intel DH55HC
Windows 7 professional 6.1.7600
Powerchute personal edition 2.2

Best regards,
Matthijs Tinholt

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:45 AM . Last Modified: ‎2024-03-22 01:14 AM

0 Likes
0
1178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:45 AM . Last Modified: ‎2024-03-22 01:14 AM

Hello,

I have installed a APC xxx UPS inline with a PC and want to reach the following functionality;

When power swichtes on, PC should boot and run, if power fails PC should shut down immediately. When power switches on again the PC should boot up.

Through the PowerChute software I was able to have the PC shutdown (hibernation switched off in Win7). The minimum time for this seems to be a minute. Is it possible to reduce this to 'immediate' or x seconds?

When the PC switches off, a dialog is offered. Users are able to abort the shutdown, Can I disable this?

When the power is back, the PC should boot again. Before (without UPS) we reached this by setting the option 'Boot After power failure' in the Intel Bios to [power on]. Unfortunatly with the UPS installed, when it switches off the PC, the power is not taken away from the outlet. Hence the motherboard does not sense that the power has been away and does not reboot after the power has been put back to the UPS. Is there a known workaround for this?


My current system configuration:
APC BK650I
Motherboard Intel DH55HC
Windows 7 professional 6.1.7600
Powerchute personal edition 2.2

Best regards,
Matthijs Tinholt

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:45 AM . Last Modified: ‎2024-03-22 01:14 AM

0 Likes
0
1178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:45 AM . Last Modified: ‎2024-03-22 01:14 AM

Hi JonPro,

Thanks for your quick reply! I can understand a little bit better now how the process is hung together.

I did a little test and indeed the timeout of the UPS seemed to be what I missed in the first tests. I can see that after a while the 'On line' and the 'overload' LED start blinking and after a few seconds the UPS is completely shut down and power is removed from its outlets (I should have been more patience with my first tests ;-). If I apply power to the UPS after the power down, the PC starts booting also because it sensed the blackout.

Only problem would now be that the timeout of the UPS is much longer than it takes (my) windows 7 machine to shut down. Is there a way to tweak this time? Problem is that we like to tell people to reset everything by turning the mains power off and on, but with the long timeout the results of this are unpredictable.

BTW: I have solved the 'problem' that the minimum setting for 'Keep my computer on as long as possible/remaining battery runtime' couldn't be set bigger than 8 minutes by changing the border values in the registry.. hope this is ok with you.

Regards!
Matthijs

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:45 AM . Last Modified: ‎2024-03-22 01:14 AM

0 Likes
0
1178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:45 AM . Last Modified: ‎2024-03-22 01:14 AM

Matt,

I haven't tried that registry hack and we do not allow our techs to make changes on the customers registry to avoid any issue that might arise. The usual shutdown delay is 2 minutes, did you set your PCPE to Keep my Computer on?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:45 AM . Last Modified: ‎2024-03-22 01:14 AM

0 Likes
0
1178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:45 AM . Last Modified: ‎2024-03-22 01:14 AM

Hi JonPro!

Indeed I'm using the 'Keep my computer on as long as possible' setting with the time set to a pretty high value (to have the PC switch off quickly after a power failure).

But then remains the problem that it takes the UPS quit some time longer than the PC to power down. And this setting can't be changed. T

We use the personal edition of the Powerchute software, is there also a professional edition that has some more settings including the ones I need?

Best regards,
Matthijs Tinholt

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:45 AM . Last Modified: ‎2024-03-22 01:14 AM

0 Likes
0
1178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:45 AM . Last Modified: ‎2024-03-22 01:14 AM

Have you tried using Preserve Battery power option? There's also a 2 minute delay before the UPS sleeps, this is to prevent any unexpected shutdown. Regarding the professional edition, we have PowerChute Business Edition and PowerChute Network Shutdown. These software would not work with BackUPS product lines, these are designed for Smart-UPS and larger UPS's and the Network Shutdown requires you to purchase/have a network management card.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:45 AM . Last Modified: ‎2024-03-22 01:14 AM

0 Likes
0
1178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:45 AM . Last Modified: ‎2024-03-22 01:14 AM

Hello,

I have installed a APC xxx UPS inline with a PC and want to reach the following functionality;

When power swichtes on, PC should boot and run, if power fails PC should shut down immediately. When power switches on again the PC should boot up.

Through the PowerChute software I was able to have the PC shutdown (hibernation switched off in Win7). The minimum time for this seems to be a minute. Is it possible to reduce this to 'immediate' or x seconds?

When the PC switches off, a dialog is offered. Users are able to abort the shutdown, Can I disable this?

When the power is back, the PC should boot again. Before (without UPS) we reached this by setting the option 'Boot After power failure' in the Intel Bios to [power on]. Unfortunatly with the UPS installed, when it switches off the PC, the power is not taken away from the outlet. Hence the motherboard does not sense that the power has been away and does not reboot after the power has been put back to the UPS. Is there a known workaround for this?


My current system configuration:
APC BK650I
Motherboard Intel DH55HC
Windows 7 professional 6.1.7600
Powerchute personal edition 2.2

Best regards,
Matthijs Tinholt

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore