BE750G: estimated battery runtime with load not living up to expectations?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BE750G: estimated battery runtime with load not living up to expectations?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
124
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:59 AM

0 Likes
7
1715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:59 AM

BE750G: estimated battery runtime with load not living up to expectations?

hello, i have a BE750G 450 Watts / 750 VA UPS:

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=BE750G-CN

while using the powerchute software, it states the following time remaing on the battery under certain loads:

229W load gives 7 min

220W load gives 8 min

157w load gives 11 min

is something wrong? the runtime chart from APC states that at 225W load there should be 12 minutes of battery time but powerchute says i'll only get 8 minutes. where did the other 4 minutes go?

http://www.apc.com/products/runtime_for_extendedruntime.cfm?upsfamily=21


P.S, here's the technical data from powerchute:


Model: Back-UPS ES 750
Serial number:
Firmware revision: 841.I3 .D
USB firmware revision: I3
Result of last manual self-test: Passed
Last manual self-test date: 04/05/2009
Last battery replacement: 11/09/2008
CPU: Intel Pentium
RAM: 2,048 MB
Free disk space: 106,430 MB
Software version: PowerChute Personal Edition 2.0
Operating system: Microsoft Windows XP (5.1.2600)


is the battery too old maybe? i just bought this yesterday. also, it's been charging since 3:30pm yesterday.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • battery
  • be750g
  • load
  • runtime
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
0
1715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

yeah i agree. but lets see how this works out and go from there.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
0
1715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

have you actually discharged the UPS and checked the actual "on battery" runtime, versus just using the software?

the software should be fairly accurate but it is most accurate while the UPS is operating on battery. the UPS may need to be "calibrated" too if this is the case. i would try discharging the UPS and actually seeing how much runtime you get on battery. again, the runtime while online is an estimate and it may take a discharge of the UPS battery to perform a little calibration to make it more accurate so the UPS realizes how much runtime it really has.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
0
1715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

i unplugged the UPS and let the computer stay on battery power. i guess i should have not let the software shut down the the PC right? that didn't calibrate anything that way.


should i cancel the ups software shutdown process? should i let the PC run until the battery dies and time that? is this bad for the computer or UPS battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
0
1715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

i would plug unplug the USB cable and all critical equipment such as the computer. if you plug in a lamp or something, let the UPS completely discharge till it turns off and then let it charge back up again with no software interaction. as long as we dont do this 10 times a day, it won't harm the UPS battery or the computer (since you shouldn't leave that plugged in so it doesnt shutdown hard).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
0
1715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

okay, just to make sure i got this right..


1) so unplug all equipment from the UPS.

2) unplug the USB cable from the UPS.

3) plug in a light bulb on the UPS.

4) unplug the UPS from the wall so it goes on battery power and let it drain via the bulb.

5) after the UPS shuts down due to being drained, plug in the UPS to the wall outlet and let it charge for a day until it has a full charge.

6) connect all equipment back into the UPS and connect the USB cable.

7) let computer start up and the UPS will self calibrate.


is this correct?

for step 5, do i have to let the UPS completely charge before plugging my equipment back into the ups and turning it on?

Message was edited by: daaan

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
0
1714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

you are exactly right! the only benefit to plugging your computer and equipment in AFTER the UPS is that if the UPS does need to go to battery, you will have the full runtime. if the battery is at 20% charge and is still charging, if the power goes out, you might drop the load if the runtime is too low. know what i mean?

the UPS should calibrate once its been draining completely and charged back up. also take note of the amount of runtime that you check with a stopwatch or something so we can compare it to the runtime chart to see if its accurate.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
0
1714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

there's just one problem though, i won't be able to emulate a sustained 225 watt load (half load for UPS unit) so there might not be a point to time the unit until shutdown. for example, even if one 40 watt bulb can last an hour, i don't think it necessarily means that two 40 watt bulbs will last for half hour. sometimes it's not linear like that.

but i will try to drain the UPS as soon as possible to see if it will self calibrate.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

0 Likes
0
1716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:42 AM . Last Modified: ‎2024-03-22 03:58 AM

yeah i agree. but lets see how this works out and go from there.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore