I have a BE550G (among others) It seems that the battery has failed. I have an extra RBC17 available. Can I use it rather than order an RBC110 ?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:29 AM . Last Modified: 2024-03-26 04:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:29 AM . Last Modified: 2024-03-26 04:15 AM
Unofficially, yes, you certainly can. The only difference in those two batteries is the stated capacity in amp-hours, with the RBC17 being a bit larger (9 AH versus 7.2 AH).
Bear in mind that I speak only as an end user and independent service provider for uninterruptible power supplies. I have no affiliation whatsoever with APC or Schneider Electric. When it comes to replacement batteries for these, I only carry the RBC17 or its generic equivalent (depending upon what the end user wants).
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:29 AM . Last Modified: 2024-03-26 04:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:29 AM . Last Modified: 2024-03-26 04:15 AM
Unofficially, yes, you certainly can. The only difference in those two batteries is the stated capacity in amp-hours, with the RBC17 being a bit larger (9 AH versus 7.2 AH).
Bear in mind that I speak only as an end user and independent service provider for uninterruptible power supplies. I have no affiliation whatsoever with APC or Schneider Electric. When it comes to replacement batteries for these, I only carry the RBC17 or its generic equivalent (depending upon what the end user wants).