BE500G3 stops randomly but no power outtage

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BE500G3 stops randomly but no power outtage
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
Dantes
Crewman Dantes
Crewman

Posted: โ€Ž2025-10-24 04:25 PM

0 Likes
5
119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-10-24 04:25 PM

BE500G3 stops randomly but no power outtage

I recently purchased the BE500G3 on Amazon. Intermittently, and without any power outages or fluctuations, the unit unexpectedly shuts off power to the connected devices and starts beeping. I only have two devices plugged into the Battery + Surge Protection outlets.
The most recent occurrence of such happened on 10/23/2025 at around 12PM local time. I live in an Silicon Valley area, California, the power from PG&E is pretty stable. 

This behavior is concerning, as the primary purpose of a UPS is to prevent loss of work during power interruptions. Instead, the unit is causing unexpected shutdowns and data loss, which defeats its intended purpose.

I understand the product includes a three-year repair or replacement warranty, and I am considering submitting a warranty claim for repair or replacement. Please advise on the appropriate next steps.

 

 

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Teken
Kirk Teken
Kirk

Posted: โ€Ž2025-10-27 04:57 AM

0 Likes
0
117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-10-27 04:57 AM

If the system is connected to a computer running APC Power Chute Software (PCPE / PCSS) provide the following logs for review: Event, Data, UPS, Diagnostics.

 

What is connected to the system now and the actual load (wattage)?

 

Questions Ask . . . ๐Ÿ‘ 

Reply

Link copied. Please paste this link to share this article on your social media post.

Dantes
Crewman Dantes
Crewman

Posted: โ€Ž2025-11-08 03:09 PM

0 Likes
1
52
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-11-08 03:09 PM

@Teken 
Thank you for your help. 
I do not have PowerChute installed anywhere. When I saw that it was discontinued I did not see the need to install it. 
At the time the incident happened, I had 1 desktop DELL_Optiplex SFF Plus 7020 with a 260W power supply unit. That does not mean that it is going to be drawing that much current all the time especially when the incident happened. 
Isnt there a log that we can extract from the DUT ? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: โ€Ž2025-11-10 06:08 AM

In response to Dantes
0 Likes
0
47
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-11-10 06:08 AM

If your specific model had a LCD Menu you could view the active fault / error codes. Since it doesnโ€™t you would have to rely on the LED / Beeper and reference the user manual as to the problem.

 

As such connecting the unit to a computer running APC Power Chute (PCPE / PCSS) would offer more insight.

 

Questions Ask . . . ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

Dantes
Crewman Dantes
Crewman

Posted: โ€Ž2025-11-12 06:48 PM

0 Likes
1
18
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-11-12 06:48 PM

@Teken I can install the APC Power Chute (PCPE / PCSS) for monitoring the UPC. 
Can you please confirm that it supports BE500G3 ? If the BE500G3 USB port is connected to the PC then it would detect and monitor it ? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: โ€Ž2025-11-12 11:14 PM

In response to Dantes
0 Likes
0
17
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-11-12 11:14 PM

Yes, the latest Power Chute Software (PCSS) is supported for your model.

 

https://www.se.com/us/en/product/BE500G3/apc-backups-500va-300w-floor-wall-mount-120v-6x-nema-515r-o...

 

Questions Ask . . . ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.