BE325R battery/surge protector

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BE325R battery/surge protector
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-27 03:33 AM

0 Likes
7
1372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-27 03:33 AM

BE325R battery/surge protector

 i have a be325r apc battery/surge protector. Just purchased a replacement battery since the battery was dead. I checked the voltage 12.5+ V on the new battery, but the "battery & Surge Protection" ports still have no voltage across them. Only the Surge Proection ports. Any ideas on what the problem could be?

Glenn

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • backup
  • be325r
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
0
1372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-27 03:32 AM

I likewise have that problem. I have four APC BE325R UPS/Surge Protector units that the batteries recently gave out, and I just bought three new Duracell 12v replacements.

Only the surge protector outlets work, and no green light or beeps showing the unit is operating. I don't know if there is some kind of reset procedure to go through, but it's odd that all four units don't work with the exact new replacement batteries that show 12+ volts with a voltmeter. 

See Answer In Context

  • Tags:
  • be325r
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-27 03:33 AM

0 Likes
0
1372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-27 03:33 AM

When you say "because the battery was dead" - how did you identify that as the problem? Or was this behavior existent prior and you thought it was because the battery was dead?

Assuming the UPS is powered on, plugged in, and not operating on battery power, there should be power to those outlets I believe. If there is not, then I am curious to confirm if you noticed this before replacing the battery or only afterwards?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-27 03:33 AM

0 Likes
0
1372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-27 03:33 AM

I checked the voltage on the battery. I don't recall if the outlets stopped working before the battery went dead. It was unused for over a year when I replaced the battery in it this week. I was planning on taking it apart to see if there was a fuse in it which was blown ,but I figured  I would ask the forum first. Maybe the transformer went bad?  Should I check certain components inside other than the fuse (if any) and the transformer?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
0
1372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-27 03:32 AM

Hmm I am not sure personally. We don't service/repair this type of unit or provide any schematics for them. If anyone else wants to chime in and help at their own risk, then please feel free.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-27 03:32 AM

I likewise have that problem. I have four APC BE325R UPS/Surge Protector units that the batteries recently gave out, and I just bought three new Duracell 12v replacements.

Only the surge protector outlets work, and no green light or beeps showing the unit is operating. I don't know if there is some kind of reset procedure to go through, but it's odd that all four units don't work with the exact new replacement batteries that show 12+ volts with a voltmeter. 

  • Tags:
  • be325r
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
0
1372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:28 AM . Last Modified: ‎2024-03-27 03:32 AM

I am experiencing the same issue. Do we have a resolution? I would be interested in either scenario (battery not working before and battery not working after).

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
0
1372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-27 03:32 AM

Bump

 

Is anyone from APC monitoring this forum?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-27 03:32 AM

0 Likes
0
1372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:29 AM . Last Modified: ‎2024-03-27 03:32 AM

thanks for starting this thread: I am facing probably a similar issue. Unit bought in beginning of 2020.

Stopped working a few weeks ago with long ongoing beep. After unplugging, checking battery connection, checking interruptor-switch (was not active): "silent & nothing".

(The non-battery-backed power outlets work though.) 

So, faulty unit & warranty or what did you all do with your units? 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore