BE325R Clicking!

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BE325R Clicking!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:37 AM

0 Likes
9
1624
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:37 AM

BE325R Clicking!

BE325R is acting up:
Erratic quick clicking noise (from relay within obviously)
AC Volatge readings at battery-backed up sockets...
Fluctuates from 121V hot-to-neutral 54V hot-to-ground 73V neutral-to-ground to something less* during click
Battery reads 13V DC
Any ideas? Is this unit toast?
It was only protecting 1 PC.
Always sounded alarm when washing machine came on, but other than that it was ok.
Thanks for any help.

*Can't be sure of low readings as digital VOM is too slow to react

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • be325r
  • clicking
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:52 PM . Last Modified: ‎2024-03-22 04:36 AM

0 Likes
0
1622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:52 PM . Last Modified: ‎2024-03-22 04:36 AM

Thanks... thought that would be the case!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:37 AM

0 Likes
0
1622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:37 AM

The clicking sound from the BE325R can be caused by laser printers injecting noise into the 110 vac line. The BE325R is apparently trying to compensate for the noisy AC by switching between line and battery power. I have a SOHO Brother printer which causes the BE325R to click constantly when it's plugged into a wall socket that shares the same AC branch the BE325R is plugged into (same room, same wall, etc.).

Reply

Link copied. Please paste this link to share this article on your social media post.

EZ_Button_apc
Commander EZ_Button_apc
Commander

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:37 AM

0 Likes
0
1622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:37 AM

Generally this happens when you have slightly dirty power. It's a pretty common occurence. The UPS is simply sensing a slight power problem, switching to battery, then immediately switching back to normal mode. When you are at a borderline condition, you will simply only hear that clicking.

It could possibly go away in the near future and just be a temporary issue. I'd also suggest trying the unit in another outlet or other circuit to see if the clicking occurs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:37 AM

0 Likes
0
1622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:37 AM

Thanks EZ.
The clicking is constant, although random.
I have moved the unit to another circuit... same thing (without load).
Voltage readings got cut off in my original posting...
Is it normal to have 121V AC across hot/neutral, but 70VAC hot/ground and 54VAC neutral/ground?
These readings dip when the click occurs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:37 AM

0 Likes
0
1622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:37 AM

70VAC between hot-ground means one thing which is a high resistence ground path. Bad wiring, bad connections, rusted wires, rusted grounding rods, can cause this. If you leave your ground the way it is now, it can pose a safety risk for people and for your electronics and also having a neutral wire with a 54V potencial in relation to ground, is not good either. The difference between Neutral and Ground should be ideally at 0 volt, they should be at the same potential, specially for sensitive electronics.

You should call an electrician as soon as possible, both situations are not good.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:37 AM

0 Likes
0
1622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:37 AM

RAU -

Thanks for your reply & concern, but the readings I provided were only evident at the OUTPUT of the BE325R.
The outlet to which it is plugged in reads normal.
Guess it isn't a battery problem, no?
Can my BE325R be fixed?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:37 AM

0 Likes
0
1622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:37 AM

oh, i know what you problem is!

the polarity inside your wall outlet is reversed. Check if your outlet follow this pattern below, if not, change it and this problem will be solved:

http://tbn0.google.com/images?q=tbn:Q__cH8wcTB8e4M:http://www.tangible-technology.com/power/p2/7_out...

But I guess the reading between Hot and Neutral and Hot-Ground should be the same even with the polarities reversed. Check it anyway.

Message was edited by: rau

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:36 AM

0 Likes
0
1622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:51 PM . Last Modified: ‎2024-03-22 04:36 AM

Nope... wall outlets are fine. Correect polarity & grounded.
It's the UPS.
Question is, is it fixable?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:52 PM . Last Modified: ‎2024-03-22 04:36 AM

0 Likes
0
1622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:52 PM . Last Modified: ‎2024-03-22 04:36 AM

I made a confusion here. The same thing happens when you plug a 220V to 110V transformer when the polarities are reversed... Since where I live is 220V and I've seen this happen before and I forgot the fact you're live in a 120V land I had thought that problem would be the polarities...

Well, electronics are always fixable, what you have to check is if it is fixable at a reasanable cost. In some countries like mine most of the times it's cheaper to fix things than to buy a new one, in US I know sometimes it's cheaper to buy a new one than to fix it. I also know that APC has a policy of changing the whole the UPS "logic" board and put a new one or exchange the whole UPS when this happens and not only the faulty component, APC does the same thing here. So, call APC and see what they tell you because your UPS is defective for sure and I'm almost certain it is not the battery that is causing this.

Message was edited by: rau

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:52 PM . Last Modified: ‎2024-03-22 04:36 AM

0 Likes
0
1623
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:52 PM . Last Modified: ‎2024-03-22 04:36 AM

Thanks... thought that would be the case!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore