My new BACK-UPS RS900 stays on battery when the genertator is running.
I have the sensitivity set to "LOW" and the generator (15 KW) is within specs (59-61 Hz, 120V +/- 10V).
The software indicates that electrical noise is the problem.
What noise is it complaining about?
Is there a way to change the sensitivity below the low setting (or turn it off)?
My 3 other UPS (two SMART-UPS 420s and a SMART-UPS 900) work well with the generator (reduced sensitivity).
What more can I do?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:48 AM . Last Modified: 2024-03-22 01:11 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:48 AM . Last Modified: 2024-03-22 01:11 AM
My new BACK-UPS RS900 stays on battery when the genertator is running.
I have the sensitivity set to "LOW" and the generator (15 KW) is within specs (59-61 Hz, 120V +/- 10V).
The software indicates that electrical noise is the problem.
What noise is it complaining about?
Is there a way to change the sensitivity below the low setting (or turn it off)?
My 3 other UPS (two SMART-UPS 420s and a SMART-UPS 900) work well with the generator (reduced sensitivity).
What more can I do?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:48 AM . Last Modified: 2024-03-22 01:11 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:48 AM . Last Modified: 2024-03-22 01:11 AM
My new BACK-UPS RS900 stays on battery when the genertator is running.
I have the sensitivity set to "LOW" and the generator (15 KW) is within specs (59-61 Hz, 120V +/- 10V).
The software indicates that electrical noise is the problem.
What noise is it complaining about?
Is there a way to change the sensitivity below the low setting (or turn it off)?
My 3 other UPS (two SMART-UPS 420s and a SMART-UPS 900) work well with the generator (reduced sensitivity).
What more can I do?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of