BACK-UPS ES - BE850G2-UK overloaded even with nothing attatched.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BACK-UPS ES - BE850G2-UK overloaded even with nothing attatched.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Markusdyer
Crewman Markusdyer
Crewman

Posted: ‎2024-06-12 02:19 AM

0 Likes
4
1072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-12 02:19 AM

BACK-UPS ES - BE850G2-UK overloaded even with nothing attatched.

I purchased a BACK-UPS ES - BE850G2-UK in February 2022. This week it is giving the long continuous beep of an overloaded device, even without any devices connected to it. 
I have checked with PowerChute software and it states the battery is 100% charged and running on AC power whilst connected and correctly states battery when unplugged. 

 
However, when I click the power button, after a few seconds, the continuous beep occurs and the software states it is overloaded. The battery itself is stating 13.75 V when testing with a multimeter. PowerChute software self test also fails. 
 
Any ideas? Has the unit/battery become faulty?
Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Markusdyer
Crewman Markusdyer
Crewman

Posted: ‎2024-06-14 01:38 AM

0 Likes
2
1020
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-14 01:38 AM

Hello, Thank you. 

After speaking to a Technical Support representative is looks as though the unit is faulty. However according to support the warranty is only two years. I have been made aware of the Trade-In program for 25% off a new device.

 

Quite disappointing that the warranty was not three years as stated in documentation. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Teken
Kirk Teken
Kirk

Posted: ‎2024-06-12 05:26 AM

0 Likes
0
1058
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-12 05:26 AM

Given you’re in the UK the APC warranty is three years. Please submit a RMA with APC Technical Support in your region. 

They may send out a replacement battery or entire unit based on some basic diagnostic testing. Insure you have photos of the purchase receipt, UPS Serial number, and battery production sticker.

 

Let us know how things turn out and what they determine the fault was and their solution: Battery Replacement vs Entire Unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Markusdyer
Crewman Markusdyer
Crewman

Posted: ‎2024-06-14 01:38 AM

0 Likes
2
1021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-14 01:38 AM

Hello, Thank you. 

After speaking to a Technical Support representative is looks as though the unit is faulty. However according to support the warranty is only two years. I have been made aware of the Trade-In program for 25% off a new device.

 

Quite disappointing that the warranty was not three years as stated in documentation. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-06-14 04:32 AM . Last Modified: ‎2024-06-14 04:32 AM

In response to Markusdyer
0 Likes
1
1017
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-14 04:32 AM . Last Modified: ‎2024-06-14 04:32 AM

Please upload a copy of the three year APC warranty coverage here. Insure it’s viewable on the APC Forum. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Markusdyer
Crewman Markusdyer
Crewman

Posted: ‎2024-06-17 07:07 AM

In response to Teken
0 Likes
0
982
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-17 07:07 AM

Thanks for replying Teken. I have been made aware that the warranty is only 3 years for EU countries. As I am in the U.K. it is only 2 years. You can close this thread if you wish. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore