Hi everybody,
We have an SC1500 UPS connected to a managed switch (Catalyst 1000 series) with no DHCP service; and we need to connect it to the network using a static IP address to monitor its status.
Is it possible to assign it a static IP address from the switch side? I already tried with arp command to associate its MAC with an IP address, and also added its MAC to the MAC address table, but I still cannot ping the UPS; which means it didn't get the IP from the switch correctly.
arp 10.100.80.191 12ab.47dd.ff89 arpa
mac-address-table static 12ab.47dd.ff89 vlan 1 interface gigabitethernet1/5/0
What am I missing here?
Notes:
- the UPS has only the SmartConnect slot and does not have the NMC card.
- with DHCP, the UPS gets an IP automatically and I can Ping it normally; but with static IP it should be similar but no luck so far.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-12 01:08 PM
@Anonymous user
You cannot set a static IP on a SMC SmartConnect UPS without DHCP and a router.
The information is published in Schneider Electric FAQ FA321794.
Link copied. Please paste this link to share this article on your social media post.