Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

All backups not coming online.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • All backups not coming online.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:12 PM . Last Modified: ‎2024-03-25 11:15 PM

0 Likes
4
1391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:12 PM . Last Modified: ‎2024-03-25 11:15 PM

All backups not coming online.

Last night, during an electrical storm, all three of my backups (Back-UPS RS 800) went into backup mode and stayed that way. As far as I can tell there was not interruption of power, though, because none of the clock radios in the house were blinking afterward and the backups are not all on the same circuit. I have since, tried unplugging them, deep cycling them, cutting off all breakers but one, etc. They still refuse to come online, as though they're not even plugged in. Any suggestions?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:13 PM . Last Modified: ‎2024-03-25 11:15 PM

0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:13 PM . Last Modified: ‎2024-03-25 11:15 PM

So last night I got home with a battery of tests in mind, and all three of them came on line as normal. Its a little unsettling that they didn't work from 3am to 8:30am yesterday morning, then suddenly worked. I never had the chance to diagnose exactly what was going on. I hope the problem is gone for good. Thanks for your help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
TheNotoriousKMP_apc
TheNotoriousKMP_apc
Contributor

Posted: ‎2021-06-28 10:12 PM . Last Modified: ‎2024-03-25 11:15 PM

0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:12 PM . Last Modified: ‎2024-03-25 11:15 PM

It's possible that there's still electrical noise on the lines. Have you tried adjusting the sensitivity on each of the UPS's to low? With excessive harmonic distortion, it's possible that the UPS will remain on battery until it sees a cleaner input.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:12 PM . Last Modified: ‎2024-03-25 11:15 PM

0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:12 PM . Last Modified: ‎2024-03-25 11:15 PM

I haven't tried using power chute yet. I'll try changing the sensitivity when i get home. I'm worried that doing that will work. Would I need to call an electrician if that is the problem? I'm guessing I wouldn't want to just run them at low sensitivity...

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
TheNotoriousKMP_apc
Contributor

Posted: ‎2021-06-28 10:12 PM . Last Modified: ‎2024-03-25 11:15 PM

0 Likes
0
1392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:12 PM . Last Modified: ‎2024-03-25 11:15 PM

You can have them take a look at it, but from what I've experienced in the past, the level of harmonic distortion that's being passed through isn't high enough to be anywhere near damaging. The electric company may look at it and decide to do nothing about it, because it's within spec.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:13 PM . Last Modified: ‎2024-03-25 11:15 PM

0 Likes
0
1393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:13 PM . Last Modified: ‎2024-03-25 11:15 PM

So last night I got home with a battery of tests in mind, and all three of them came on line as normal. Its a little unsettling that they didn't work from 3am to 8:30am yesterday morning, then suddenly worked. I never had the chance to diagnose exactly what was going on. I hope the problem is gone for good. Thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore