APV9602

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APV9602
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
125
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
mwitt
Crewman mwitt
Crewman

Posted: ‎2024-05-02 05:55 PM

0 Likes
4
1055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-02 05:55 PM

APV9602

Has anyone encountered an issue with the APV9602 NMC resetting to default on every power cycle of the NMC. We have had this on multiple occasions and have found the only fix to replace the nmc

 

UPS installed SMV750CAI

NMC: APV9602

MNC Firmware: 3.7.APC9602.APC.191211

 

We had the NMC operating fine holding a static IP and username & password, after a planned site outage for a few weeks the NMC now reverts to defaults every time static IP settings are applied (and performs its reboot) / network cable is removed including the username settings 

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: ‎2024-05-03 06:36 AM

0 Likes
1
1030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-03 06:36 AM

If the hardware is still under APC Warranty I would recommend you contact their Technical Support for insight & guidance.

 

Regardless, a few things to consider and answer in no specific order of importance.

 

- Have you reset the NMC to a default state? Doing so will ensure there are no programming conflicts.

 

- LED Status: What are the LED color status when this problem occurs? 

- DHCP Reservation: Have you tried to reserve the MAC Address for the IP to see if there is a difference in behaviour?

 

Logs: What do the logs show about the NMC and its operations? Do you see any cold reboots, watch dog errors, internal battery fault, NTP errors?

 

Testing: Once the NMC is in a default state using DHCP MAC Reservation. Create a new Admin account and validate you can login using those credentials. Change the APC password to something else.

 

Once that is done remove the NMC to replicate a power loss. Wait 60 seconds and inset the NMC and wait for it to reboot.

 

Once it’s online check to see if the two user accounts are present and accessible. If they are rinse and repeat the process by removing the NMC for a longer period from 10 - 60 minutes. If the two accounts are still accessible you can make all the network changes you require for proper operations.

 

If after making the same changes the NMC loses its stored programming you’ll need to identify the conflicts.

 

Start there and let me know what you observe. 👍

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Teken
Kirk Teken
Kirk

Posted: ‎2024-05-03 06:36 AM

0 Likes
1
1031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-03 06:36 AM

If the hardware is still under APC Warranty I would recommend you contact their Technical Support for insight & guidance.

 

Regardless, a few things to consider and answer in no specific order of importance.

 

- Have you reset the NMC to a default state? Doing so will ensure there are no programming conflicts.

 

- LED Status: What are the LED color status when this problem occurs? 

- DHCP Reservation: Have you tried to reserve the MAC Address for the IP to see if there is a difference in behaviour?

 

Logs: What do the logs show about the NMC and its operations? Do you see any cold reboots, watch dog errors, internal battery fault, NTP errors?

 

Testing: Once the NMC is in a default state using DHCP MAC Reservation. Create a new Admin account and validate you can login using those credentials. Change the APC password to something else.

 

Once that is done remove the NMC to replicate a power loss. Wait 60 seconds and inset the NMC and wait for it to reboot.

 

Once it’s online check to see if the two user accounts are present and accessible. If they are rinse and repeat the process by removing the NMC for a longer period from 10 - 60 minutes. If the two accounts are still accessible you can make all the network changes you require for proper operations.

 

If after making the same changes the NMC loses its stored programming you’ll need to identify the conflicts.

 

Start there and let me know what you observe. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Antonio_Pena
Antonio_Pena
Cadet

Posted: ‎2024-05-31 12:54 AM

In response to Teken
0 Likes
0
951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-31 12:54 AM

Hi,

I have the same problem with our APV9602 cards.

They are lossing the user configurations: static IP,  password, ...

It seems they have some internal HW or SW issue.

I suppose more people in the world have the same problems with these SNMP agent cards.

Has Schneider R&D department some solution for this common issue?

Thanks in advance for your answers.

Best regards.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Antonio_Pena
Antonio_Pena
Cadet

Posted: ‎2024-05-31 01:08 AM

0 Likes
1
951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-31 01:08 AM

Hi,

I've encountered the same issue in APC net cards.

They are lossing configurations and go to default values after power restart.

Do you know how to solve it?

Best regards.

Antonio.

Reply

Link copied. Please paste this link to share this article on your social media post.

mwitt
Crewman mwitt
Crewman

Posted: ‎2024-06-05 01:38 PM

In response to Antonio_Pena
0 Likes
0
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-05 01:38 PM

Hi Antonio,

 

The closest thing to solving it I have had is to log into the GUI when it assigned to a DHCP address and perform a factory reset. After the factory reset I was able to change password and IP address and it held that information on reboot. The one I did this to survived a reboot a week later also.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore