APC UTS6H and APC UPS - Site Wire Error

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC UTS6H and APC UPS - Site Wire Error
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
wicked_apc
wicked_apc
Cadet

Posted: ‎2021-06-29 11:21 PM . Last Modified: ‎2024-03-20 12:40 AM

0 Likes
5
1527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:21 PM . Last Modified: ‎2024-03-20 12:40 AM

APC UTS6H and APC UPS - Site Wire Error

Hi, I have a question about using an APC UPS with an APC UTS6H that I hoping you can help me answer. 

The UTS6H has been working fine with my EU2000i so far, so I decided to add an APC UPS.

I understand you can plug the UPS into the convenience plug on the front for power from circuit 1.  Initially I plugged the UPS into a home outlet for initial testing and things were fine, I even ran a test by turning off utility power and things worked great.

Once testing went well I set it up close to the UTS6H and plugged it into the convenience plug - the APC UPS self tested ok but I am now getting a "site wiring" error.

APC site says its due to one of the following conditions:

1. Overloaded neutral wire (>5vdc measured between Neutral and Ground).

2. Reversed polarity (hot and neutral wires are reversed).

3. Missing ground wire. (Note: this also includes using a 3 prong to 2 prong adapter)

I confirmed its not #1 or #2 which makes me focus on #3.  I see that the convenience plug is grounded to the UTS chassis as everything else is. 

I know the UTS has the white/neutral to the panel, do I need to ground the chassis of the UTS to the panel via a copper wire?

any other thoughts or suggestions?


Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 11:22 PM . Last Modified: ‎2024-03-20 12:40 AM

0 Likes
0
1527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:22 PM . Last Modified: ‎2024-03-20 12:40 AM

You're welcome! Glad I could help.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:21 PM . Last Modified: ‎2024-03-20 12:40 AM

0 Likes
0
1527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:21 PM . Last Modified: ‎2024-03-20 12:40 AM

Hello,

The neutral bus in the UTS is grounded to earth ground through the electrical panel, neutral to ground bond.

Also, I discussed with a co-worker and we came up with some questions.

  • Please confirm what UPS model you're using. The model should be on a white sticker on the back or bottom of the unit.
  • Is the UPS directly connected to the convenience outlet (no adapters, extra cabling, etc)
  • Confirm that the Honda generator is not independently grounded.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:21 PM . Last Modified: ‎2024-03-20 12:40 AM

0 Likes
0
1527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:21 PM . Last Modified: ‎2024-03-20 12:40 AM

Has this question been answered/resolved ?

I have the exact same problem with a UTS-10BI.

The front panel convenience outlet checks fine on a test set for hot/neutral/ground/polarity. Yet the Smart UPS 1500 reports a "site wiring fault". Also a PRO-8T2 surge strip illuminates it's "building wiring fault" indicator when plugged into the same front panel convenience outlet. The outlet does work properly, the UPS picks up the load with no interruptions. There are no additional cables or adaptors between it and the outlet.

Continuity of the white neutral wire from the UTS-10BI to the main panel neutral/ground bond was checked and is good.

There are no error indications on the UTS-10BI front panel.

Measuring voltage at the convenience outlet between ground/neutral is approximately 150 volts and fluctuates.

Primary neutral bond at main panel is good.

UTS-10BI was manufactured in 2/2013.

Do I have a defective transfer switch ? I checked the main board, there does not appear to be anything obvious (ie. burnt traces, etc) - the unit functions fine with the exception of that convenience outlet not being liked by the Smart UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 11:21 PM . Last Modified: ‎2024-03-20 12:40 AM

0 Likes
0
1527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:21 PM . Last Modified: ‎2024-03-20 12:40 AM

Is this a new installation or has the condition developed after previously working properly?

Neutral and ground internal to the UTS are isolated from each other as required by the National Electrical Code. As you have already verified, the neutral connection to your main panel is provided by the white wire(s) in the UTS flexible conduit. The ground connection from the UTS to the main panel is made through the metal to metal contact of the flexible metal conduit itself. Since you have measured 150 volts between ground and neutral at the UTS convenience outlet, I would suggest you measure for voltage from the flexible conduit to ground at both the UTS end and the main panel. If you find one end that does read voltage on the conduit you should check for a clean, bare (paint free) contact between the conduit connector and the case of the box in question. Another remote possibility is that your main panel case is not properly bonded to ground.

If you have installed the UTS without using the provided flexible metal conduit you should make the ground connection directly using a substantial ground wire.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:21 PM . Last Modified: ‎2024-03-20 12:40 AM

0 Likes
0
1527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:21 PM . Last Modified: ‎2024-03-20 12:40 AM

Wayne, "thank you!".


That was the issue. Yes, this is a new install. We had to use a J-box to extend the UTS-10BI mounting location on another wall adjacent (perpendicular to - in a corner) to the main breaker panel. So the J-box and conduit were PVC. When I jumpered the UTS-10BI metal conduit over to the main panel with a separate wire, the "site fault indicator" on the UPS went out. I was measuring about 33 volts between the metal UTS conduit and ground on the main panel.

So I'm going to be running a #10 (or better, depending on what I have in my 'junk box') over from the ground inside the UTS10-BI over to a ground on the main panel.

The missing piece of the puzzle was I hadn't realized that ground and neutral are separate inside the UTS-10BI. So that explains the mystery, and the need for keeping them separate going to the main panel.

Thanks again for the quick response.

best regards.

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-06-29 11:22 PM . Last Modified: ‎2024-03-20 12:40 AM

0 Likes
0
1528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:22 PM . Last Modified: ‎2024-03-20 12:40 AM

You're welcome! Glad I could help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of