APC UPS switches to battery even though there is no power failure

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC UPS switches to battery even though there is no power failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
tixaport2
tixaport2
Cadet

Posted: ‎2024-04-24 09:57 AM

0 Likes
4
1855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-24 09:57 AM

APC UPS switches to battery even though there is no power failure

I bought two UPS on February, the model number are BVX700LUI-MS and BV1000I-MS. The first is connected to my iMac and a LG monitor, the second one is connected to my PS5 and WiFi router.

 

The problem occurred two weeks ago on the BVX700LUI-MS. The UPS switches to battery mode, with 4 beeps every 30 seconds even though there is no power failure in my house. I tried unplug and plug again but it stills beep. Sometimes the UPS automatically switches to power mode, and sometimes it does not.

 

The same problem just occurred yesterday with my second UPS. I noticed that it only occurs at evening, and this time in my country is summer season.

 

I am confused because these two UPS are manufactured in 2022, and just in use for about two months. I don’t know if the battery in these two were malfunction together, or the voltage in my house can lead to this behavior. I am appreciated for any help or solution. Thank you.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Teken
Kirk Teken
Kirk

Posted: ‎2024-04-25 05:00 AM

0 Likes
3
1843
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-25 05:00 AM

As a starter you should have APC Power Chute software installed. As this would inform you of the quality of power in your location or lack thereof.

 

Once you have Power Chute Software loaded and connected to a computer system. The logs more than likely will show dirty power as the main culprit.

 

Dirty power can be low / high voltage. It can be out of band frequency. It can be high THD (Total Harmonic Distortion).


It can be a rapid change in line voltage. Lastly, it can be due to a surge / brown out or what is known as a voltage rise vs voltage sag condition.

 

At the end of the day if the logs show any of the above. Guess what the UPS is doing its job in providing clean uninterrupted power to your connected devices! 👍

 

Install the software and report back whet you observe. 

Reply

Link copied. Please paste this link to share this article on your social media post.

tixaport2
tixaport2
Cadet

Posted: ‎2024-04-25 07:02 AM

In response to Teken
0 Likes
2
1792
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-25 07:02 AM

Thanks for your advise, by the way I’m using a Mac computer, and my UPS model is not supported by the Power Chute software. Is there any third party software has capability to measure those number? Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-04-26 03:24 AM

In response to tixaport2
0 Likes
1
1787
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-26 03:24 AM

The following are some freeware applications for your consideration:

 

APCUPSD, NUT, WinPower, 

Reply

Link copied. Please paste this link to share this article on your social media post.

tixaport2
tixaport2
Cadet

Posted: ‎2024-04-29 06:10 PM

In response to Teken
0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-29 06:10 PM

Just update to the topic. I bought two travel plug adapters with surge protector and use them to connect my UPS to the wall outlet. The problem didn't occur again so far. I think the main cause is electric source in my house, not from the UPS. I will observe more and update if it's happen again.

 

Anyway, thanks for your suggestion.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore