APC UPS 800VA (BE800-IND) or APC UPS Pro 1000 (BR1000G-IN)

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC UPS 800VA (BE800-IND) or APC UPS Pro 1000 (BR1000G-IN)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

0 Likes
3
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

APC UPS 800VA (BE800-IND) or APC UPS Pro 1000 (BR1000G-IN)

Hi,

My name is Aravind. I live in Bangalore, India. I need your suggestion to decide on which UPS to buy.

This is for home use. My requirement is to connect 2 laptops, 1 desktop PC (high end gaming machine), one gaming console and one LED TV. Currently I have APC UPS 500 to which I have connected all these devices using power cord extensions.

The problem I am facing is that the main power supply of the house is getting tripped when I switch on all these devices and I feel its time to upgrade the UPS.

I searched online and came across these two models - BE800-IND and BR1000G-IN. I am not able to decide which one I should buy. Please help me decide keeping my requirements in mind.

Thanks,

Aravind

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

0 Likes
0
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

Hi,

The BR1000G-IN offers 600 watts max. The SUA750i offers 500 watts max so the BR1000G-IN will sustain the load as well as the SUA750i. The one thing you should verify is if your systems work with step approximated sign wave. The Back-UPS family of UPS when on battery produce a step approximated sign wave and some computer power supplies and none computer equipment do not work well with the type of a sign wave.  With that in mind I assume that is way the sales rep suggested the Smart-UPS. Smart-UPS offer a pure sign wave while on battery so there could be an issue with the "high end gaming machine". If the system can handle step approximated sign wave then the BR1000G-IN is a good choice. If the power supply need pure sign wave then you should purchase the SUA.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

0 Likes
0
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

Hi,

Upgrading the UPS will not resolve the issue of the house circuit tripping. You need to decrease the load on that circuit. If the UPS circuit breaker is tripping then upgrading the UPS is the proper solution and I suggest purchasing the BR1000.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

0 Likes
0
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

Thanks for the reply Bill. I am just worried that connecting and running all my devices at one go with APC UPS 500 may cause some damage to the devices. Although I hardly run all those devices at once, at any given time either the laptops or the TV/Game Console will be in use. Have not seen any problem so far.

The APC sales guys are pushing me to go for SUA 1000i or SUA 750i which I feel are way beyond for my requirement and they are very costly as well. So can I say here that BR1000 is sufficient?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

0 Likes
0
988
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:09 AM . Last Modified: ‎2024-03-20 12:22 AM

Hi,

The BR1000G-IN offers 600 watts max. The SUA750i offers 500 watts max so the BR1000G-IN will sustain the load as well as the SUA750i. The one thing you should verify is if your systems work with step approximated sign wave. The Back-UPS family of UPS when on battery produce a step approximated sign wave and some computer power supplies and none computer equipment do not work well with the type of a sign wave.  With that in mind I assume that is way the sales rep suggested the Smart-UPS. Smart-UPS offer a pure sign wave while on battery so there could be an issue with the "high end gaming machine". If the system can handle step approximated sign wave then the BR1000G-IN is a good choice. If the power supply need pure sign wave then you should purchase the SUA.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore