New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
APC Pro 1500 S Stuck in F02 Error Mode with Constant Beeping
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-2005:56 PM
APC Pro 1500 S Stuck in F02 Error Mode with Constant Beeping
I have an APC Pro 1500 S that randomly tripped while I was at work and stayed beeping for hours (my dog is now traumatized to the beeping sound).
No matter what I do the unit only shows F02 with a constant beeping. I've replaced the battery, let the whole unit discharge without the battery connected, and several other ideas I found online.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-2205:28 AM
The F02 code indicates there is a short connected to the units outputs. Remove AC Mains from the wall outlet. Disconnect all connected loads from the rear of the unit.
Disconnect the battery and than press and hold the power button. You may hear a click / beep when this is done. You may not hear anything at all either. ☝️
Reconnect the battery and apply AC Mains to the unit and power on. How does the unit behave now without ANYTHING attached to the outputs?