APC NS 40 reports wrong load percentage

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC NS 40 reports wrong load percentage
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Janeway Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

0 Likes
6
1466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

APC NS 40 reports wrong load percentage

Last week i purchased APC BackUPS NS 40 to replace 8 years old APC UPS that has failed. There are three devices on the UPS: cable modem, unmanaged 8 port gigabit switch and linux machine that acts as firewall and a router between our LAN and the rest of the world.

These three devices together draw between 49 and 67 watts of power depending on the network traffic, but the UPS reports only 5% load and 67 minutes of battery runtime remaining. According to the specs sheet for the UPS, the output power capacity is 257W/450VA, so i'd expect the load to be roughly between 19% and 27% and the battery runtime to be at most 16 minutes. I have double checked that the devices are indeed plugged into the UPS, and that they are plugged into the power backup side of it. I have also put load on the linux machine (recompiling kernel) to see if the load percentage changes, and it did not.

While this is not a critical problem, i'd like to get it sorted out eventually. If anyone has any ideas on how to fix this, I'd appreciate them.

Thanks.

I'm including the output of 'apcaccess status' from the linux machine:

APC      : 001,034,0839
DATE     : 2015-07-06 11:03:34 -0400
HOSTNAME : xxxxxxxxxxxxxx
VERSION  : 3.1
UPSNAME  : Back-UPS NS 4001
CABLE    : USB Cable
DRIVER   : USB UPS Driver
UPSMODE  : Stand Alone
STARTTIME: 2015-07-06 10:22:53 -0400
MODEL    : Back-UPS NS 4001
STATUS   : ONLINE
LINEV    : 121.0 Volts
LOADPCT  : 5.0 Percent
BCHARGE  : 101.0 Percent
TIMELEFT : 67.7 Minutes
MBATTCHG : 10 Percent
MINTIMEL : 3 Minutes
MAXTIME  : 0 Seconds
SENSE    : High
LOTRANS  : 92.0 Volts
HITRANS  : 139.0 Volts
ALARMDEL : 30 Seconds
BATTV    : 13.4 Volts
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT  : 0 Seconds
CUMONBATT: 0 Seconds
XOFFBATT : N/A
STATFLAG : 0x05000008
SERIALNO : 4B1507P56665
BATTDATE : 2015-02-15
NOMINV   : 120 Volts
NOMBATTV : 12.0 Volts
FIRMWARE : 903.K3 .D USB FW:K3
END APC  : 2015-07-06 11:03:39 -0400

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

0 Likes
0
1466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

Thank you, I will read up on them. And thank you for Your help. ๐Ÿ™‚

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

0 Likes
0
1466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

Just curious - what is telling you the load is 49-67 watts that you're comparing against?

I was also thinking, can you pull the plug on the UPS and see if the reading changes while it is on battery, for kicks?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

0 Likes
0
1466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

On 7/6/2015 2:55 PM, Angela said:

Just curious - what is telling you the load is 49-67 watts that you're comparing against?

I used kill-a-watt to measure the wattage. About 6 months ago when I upgraded the linux machine from P3 to G645, I was curious about how much the power usage would drop, and the old P3 was 100W higher than the G645. That's a nice chunk in savings, that machine is always running.

On 7/6/2015 2:55 PM, Angela said:

I was also thinking, can you pull the plug on the UPS and see if the reading changes while it is on battery, for kicks?

That was a good catch, the UPS seems to only report the load correctly when on battery power, after I plugged it back in, it just stays at whatever percentage it was at when the power was out.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

0 Likes
0
1466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

Ahh, ok. I asked for you to pull the plug because this type of UPS (it is similar to our Back-UPS ES) uses a standby topology. Someone told/reminded me a little bit ago these UPSs can only detect an overload while on battery power due to the Standby topology design. Thus, I figured that means it can only accurate detect the load %/W while on battery power.

(Here is a white paper on UPS systems if you're interested in further detail regarding standby design -> http://www.apc.com/whitepaper/?wp=1 )

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

0 Likes
0
1466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

Thanks, makes sense, i didn't even consider active vs passive UPS when i bought the darn thing, guess i'll have to put this one on less important equipment and go get a SmartUPS instead.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

0 Likes
0
1466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

I think that Line Interactive topology units would be an option for you. We have line interactive design Back-UPS like Back-UPS XS or RS/Pro. Or, next higher up would be Smart-UPS SMC depending on what your other requirements are.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

0 Likes
0
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-07-11 10:54 PM . Last Modified: โ€Ž2024-03-19 11:48 PM

Thank you, I will read up on them. And thank you for Your help. ๐Ÿ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now