APC ES 750 Not Charging and Shutting Down During Power Fluctuations

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC ES 750 Not Charging and Shutting Down During Power Fluctuations
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

0 Likes
6
2103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

APC ES 750 Not Charging and Shutting Down During Power Fluctuations

Whenever I get some kind of power fluctuations the es750 no longer switches over to battery - it just shuts down. I first thought this was a battery problem so I changed the battery. Still the same results.

Other things is that I notice is the battery is always "charging". The battery charge is 14% but the estimated battery time is 2mins. Never changes - I even powered off my devices and tried to let it charge overnight. Load on the battery is pretty low.

Serial number:4B0736P72082
Firmware revision:841.I1.D

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

0 Likes
0
2102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

Yes - seems like the battery is not charging so any transfer to battery results in a load drop because it cannot output any voltage while running on battery.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

0 Likes
0
2102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

Whenever I get some kind of power fluctuations the es750 no longer switches over to battery - it just shuts down. I first thought this was a battery problem so I changed the battery. Still the same results.

Other things is that I notice is the battery is always "charging". The battery charge is 14% but the estimated battery time is 2mins. Never changes - I even powered off my devices and tried to let it charge overnight. Load on the battery is pretty low.

Serial number:4B0736P72082
Firmware revision:841.I1.D

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

0 Likes
0
2102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

Hi javand

Can you clarify - does the UPS itself turn off during the fluctuation or just your attached devices? Do you know when this started?

I am wondering if the battery charger is no longer functioning for some reason.

Have you tried a pull plug test with a lamp/radio, etc or another non critical load? (i'd also remove the data cable from the UPS at this time). just curious but based on what you're saying, it seems like the entire UPS is turning off vs. just the attached load. and during a pull plug test, i'd expect the same, again, assuming the problem here is that the UPS is not charging the battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

0 Likes
0
2102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

Yeah to clarify- 

The UPS doesn't shut down, however the attached devices are immediately shut off as if someone pulled the plug. I've had the UPS for approximately 5 years now so it started happening about 4 months back. I thought the problem was the battery - but as I previously mentioned I replaced that.

I have tried the pull plug test with a mobile device charger...it seemed to power the charger for a mere couple of seconds. Battery charge doesn't seem to ever go higher than 7%.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

0 Likes
0
2102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

After consulting with SecretSquirrel, this seems like a charger fault on the UPS unfortunately. We were both a little surprised PowerChute is not reporting some type of 'internal fault' to indicate a UPS problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

0 Likes
0
2102
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

In fact...last time I ran the self-test it immediately shut down my system. But when you view the history via PowerChute it doesn't report anything - as if nothing ever happened.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

0 Likes
0
2103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-29 10:18 PM . Last Modified: ‎2024-03-19 11:39 PM

Yes - seems like the battery is not charging so any transfer to battery results in a load drop because it cannot output any voltage while running on battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore