Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

APC ES 350, constant tone, no light

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC ES 350, constant tone, no light
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:30 AM . Last Modified: ‎2024-03-22 01:25 AM

0 Likes
3
2733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:30 AM . Last Modified: ‎2024-03-22 01:25 AM

APC ES 350, constant tone, no light

Hi all, got a recurring, constant issue that is becoming especially frusterating.

I've got 7 or 8 350 UPCs here that are all suffering from the same symptomes.

When powered on, the unit will beep once, I hear a click, then the green light comes one, then it goes off and a constant tone will sound.

If I understand correctly it means that the unit is overloaded.

However there is nothing plugged into it!

I have attempted to do the step in post #3 here :http://forums.apc.com/spaces/9/struxureware-for-data-centers/forums/general/4964/isx-manager-ping-fa...

but to no avail.

So, I've got, Constant Tone and no Light, with no load on the system. There is a new battery in it. I have checked the user's manual, but none of the troubleshooting options apply.

I've even tried swapping PCB board between units, but it has no difference.

Anyone have any ideas?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • beeping
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:30 AM . Last Modified: ‎2024-03-22 01:25 AM

0 Likes
0
2733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:30 AM . Last Modified: ‎2024-03-22 01:25 AM

Hi all, got a recurring, constant issue that is becoming especially frusterating.

I've got 7 or 8 350 UPCs here that are all suffering from the same symptomes.

When powered on, the unit will beep once, I hear a click, then the green light comes one, then it goes off and a constant tone will sound.

If I understand correctly it means that the unit is overloaded.

However there is nothing plugged into it!

I have attempted to do the step in post #3 here :http://forums.apc.com/spaces/9/struxureware-for-data-centers/forums/general/4964/isx-manager-ping-fa...

but to no avail.

So, I've got, Constant Tone and no Light, with no load on the system. There is a new battery in it. I have checked the user's manual, but none of the troubleshooting options apply.

I've even tried swapping PCB board between units, but it has no difference.

Anyone have any ideas?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:30 AM . Last Modified: ‎2024-03-22 01:25 AM

0 Likes
0
2733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:30 AM . Last Modified: ‎2024-03-22 01:25 AM

Thanks for the help JonPro.

I also came to the conclusion that the units were toast. Nice to get some confirmation.
They are the Back-UPS ES 350.
The Dead Units are model BE350U, and one BE350U-CN

S/Ns are:
AB0446144381
AB0449141626
AB0446248687
AB0446247755
&
AB0443147022

I did manage to get new batteries into an additional 3 units(BE350U's) that are now functional.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-29 03:30 AM . Last Modified: ‎2024-03-22 01:25 AM

0 Likes
0
2733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:30 AM . Last Modified: ‎2024-03-22 01:25 AM

Thanks for giving us an update. I would like to inform you as well that if you are planning to purchase new UPS you can avail of our TradeUPS. TradeUPS works by exchanging your old, working and non-working APC or third-party UPS in exchange of a new one. To know more about Trade-UPS feel free to call our hotline 800.800.4272

JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:30 AM . Last Modified: ‎2024-03-22 01:25 AM

0 Likes
0
2734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:30 AM . Last Modified: ‎2024-03-22 01:25 AM

Hi all, got a recurring, constant issue that is becoming especially frusterating.

I've got 7 or 8 350 UPCs here that are all suffering from the same symptomes.

When powered on, the unit will beep once, I hear a click, then the green light comes one, then it goes off and a constant tone will sound.

If I understand correctly it means that the unit is overloaded.

However there is nothing plugged into it!

I have attempted to do the step in post #3 here :http://forums.apc.com/spaces/9/struxureware-for-data-centers/forums/general/4964/isx-manager-ping-fa...

but to no avail.

So, I've got, Constant Tone and no Light, with no load on the system. There is a new battery in it. I have checked the user's manual, but none of the troubleshooting options apply.

I've even tried swapping PCB board between units, but it has no difference.

Anyone have any ideas?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore