Hi All,
I work in a company where we have recently installed 40+ Smart-UPS 750's all at remote sites, each one has a SNMP/Web management card and I would ideally like someway to record the configuation of each one, so that if a device has to be replaced, the replacement can be configured before attending the remote site using the same configuration.
I understand that the management card is accessable using FTP and it is possible to download a config.ini file for a perticular device. But is there an application that anyone knows of that can make this an automatic process?? The last thing i want todo is log on to each device indivdually to back up their config.
We currently use a software package called Orion todo automate the same task on our remote routers, but that software package doesnt support getting configuations via FTP.
Any advice on how i can go about this would be greatly appreciated.
Thanks
Simon
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:11 AM . Last Modified: 2024-03-22 04:09 AM
There are many ways to automate the process. This is one way:
Download [curl from here|http://curl.netmirror.org/download.html] for your OS of choice. You want the binary package, not the source package.
Then, create a .bat or script file with lines like this:
curl ftp://apc:apc@192.168.1.100/config.ini > backup_192_168_1_100.ini
curl ftp://apc:apc@192.168.1.101/config.ini > backup_192_168_1_101.ini
curl ftp://apc:apc@192.168.1.102/config.ini > backup_192_168_1_102.ini
...
You can schedule the script file to run at certain times and I'm sure you could get fancier with timestamped logs and log rotation.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:11 AM . Last Modified: 2024-03-22 04:09 AM
There are many ways to automate the process. This is one way:
Download [curl from here|http://curl.netmirror.org/download.html] for your OS of choice. You want the binary package, not the source package.
Then, create a .bat or script file with lines like this:
curl ftp://apc:apc@192.168.1.100/config.ini > backup_192_168_1_100.ini
curl ftp://apc:apc@192.168.1.101/config.ini > backup_192_168_1_101.ini
curl ftp://apc:apc@192.168.1.102/config.ini > backup_192_168_1_102.ini
...
You can schedule the script file to run at certain times and I'm sure you could get fancier with timestamped logs and log rotation.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.