APC Back-UPS is slow to respond to power disturbance

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC Back-UPS is slow to respond to power disturbance
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
jjuly_apc
jjuly_apc
Cadet

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

0 Likes
3
1173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

APC Back-UPS is slow to respond to power disturbance

APC Back-UPS BE550G is slow to respond to power disturbance.
My computer shuts down but other devices such as
the cable modem and router continue to operate.

I am not using any power management software.

purchased Sept 2012

Looking for advise on how to proceed. I am in Panama, so bringing it to the shop is not feasible.

Computer: PC with Win7 ultimate. Power supply was replaced, but the problem persists.

John

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:02 PM . Last Modified: ‎2024-03-20 12:57 AM

0 Likes
0
1172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:02 PM . Last Modified: ‎2024-03-20 12:57 AM

You've indicated the UPS shuts down your computer. Can you verify this is a complete power off of the computer or does it reboot, powering back up to the login screen?

A complete power off would suggest a possible incompatibility between your CPU power supply and the step approximated sinewave output of the UPS. A reboot, would indicate an issue of the CPU power supplies ability to support itself during the long transfer of the UPS, from Online to Onbattery. This transfer time can be reduced slightly by adjusting the Sensitivity of this unit through PCPE or through the front display, whose process is outlined in the users manual. You may have better results once this Sensitivity has been adjusted to it's highest setting.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

0 Likes
0
1172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

silly question but did you verify the computer is plugged into a battery back up + surge outlet and not just surge only? also, you said the computer shuts down - i just want to make sure it turns off and stays off versus reboots.

depending on the answers there, your power supply maybe is too high end for this type of UPS. you may need to look into a pure sinewave UPS which generally also have a quicker transfer time to battery. that is what usually causes this type of thing assuming the computer is plugged into a battery back up outlet.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

0 Likes
0
1171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:01 PM . Last Modified: ‎2024-03-20 12:58 AM

Some computer power supplies have longer "hold time", i.e., greater storage capacity that would get you through the Back-UPS transition time.  I know you said you replaced the power supply, but it may be worth a shot at a very high quality (more expensive) power supply from a reputable vendor.  Also, even though your computer seems to work fine with, let's say, a 450 watt power supply, installing an extremely robust 1kw or 1.2kw power supply (again from a reputable vendor) would add to your computer system's "hold time" and may get you through the transition from commercial to backup power.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:02 PM . Last Modified: ‎2024-03-20 12:57 AM

0 Likes
0
1173
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:02 PM . Last Modified: ‎2024-03-20 12:57 AM

You've indicated the UPS shuts down your computer. Can you verify this is a complete power off of the computer or does it reboot, powering back up to the login screen?

A complete power off would suggest a possible incompatibility between your CPU power supply and the step approximated sinewave output of the UPS. A reboot, would indicate an issue of the CPU power supplies ability to support itself during the long transfer of the UPS, from Online to Onbattery. This transfer time can be reduced slightly by adjusting the Sensitivity of this unit through PCPE or through the front display, whose process is outlined in the users manual. You may have better results once this Sensitivity has been adjusted to it's highest setting.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore