APC Back-UPS XS 1000 and car battery!

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC Back-UPS XS 1000 and car battery!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:46 AM . Last Modified: ‎2024-03-22 01:13 AM

0 Likes
7
1707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:46 AM . Last Modified: ‎2024-03-22 01:13 AM

APC Back-UPS XS 1000 and car battery!

hi guys! Working on little project here...
Im trying to plug small tv and my xbox 360 into APC which will be connected to my car battery by 400W converter... So we can play some games while tailgating! I have APC XS1000. When I plug APC into converter(which is hooked to my car battery) Building Wiring Fault light comes on and APC remains on battery power rather than switching to on line mode. I tried to lower sensitivity and then it went online but AVR, See manual, and Building Wiring Fault light were on! Any ideas how i can get it to work?

P.S. tv and xbox combined about 250w... It works on APC battery for about 30 mins. Also if i plug xbox and tv straight to the converter it works fine so I know my car battery provides enough power for both. I just would like to have it plugged in to APC so i can see how many volts going in or out and other info that APC displays!

Thanks for all suggestions!

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • battery
  • car
  • tv
  • xbox360
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:12 AM

0 Likes
0
1708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:12 AM

I understand that, keep in mind that I'm connecting it to the car battery not outlet in my house.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:13 AM

0 Likes
0
1708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:13 AM

I understand that Emil. DC batteries only has a positive and a negative terminals, by using an inverter it provides you with an AC voltage. Have you checked the specifications of your inverter? Does it provide a step approximated sine wave or a pure sine wave? Does the inverter provides clean power/voltage/frequency that the UPS can handle? Our UPS checks the outlet where it is plugged in if there's Hot, Neutral and Ground wirings. From hot to neutral and hot to ground it is expecting to see ~120V AC while Neutral to Ground is ~0V AC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:13 AM

0 Likes
0
1708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:13 AM

Yeah it's 400w with sine wave. Is 400 not enought to power it up UPS? Is there a better way to ground it somehow?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:13 AM

0 Likes
0
1708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:13 AM

What kind of sinewave does it provide on the output? What kind of UPS do you have? Our BX1000G series supports 600Watts, you need to determine how many watts does your load consumes. If your load pulls greater than or equal to 400W it would overload your inverter causing the UPS to go on battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:12 AM

0 Likes
0
1708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:12 AM

I have ups xs1000... When I plug my xbox and tv straight to the converter it is able to pull both. But when I plug in ups all by itself with nothing plugged in to it, it stays on battery and never goes online... So I know converter is powerful enough to pull xbox and tv ( apprx 150 to 200 w).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:12 AM

0 Likes
0
1708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:12 AM

What is the exact model number of your inverter? I have a feeling that might be producing a step sine wave.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:12 AM

0 Likes
0
1708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:12 AM

hi guys! Working on little project here...
Im trying to plug small tv and my xbox 360 into APC which will be connected to my car battery by 400W converter... So we can play some games while tailgating! I have APC XS1000. When I plug APC into converter(which is hooked to my car battery) Building Wiring Fault light comes on and APC remains on battery power rather than switching to on line mode. I tried to lower sensitivity and then it went online but AVR, See manual, and Building Wiring Fault light were on! Any ideas how i can get it to work?

P.S. tv and xbox combined about 250w... It works on APC battery for about 30 mins. Also if i plug xbox and tv straight to the converter it works fine so I know my car battery provides enough power for both. I just would like to have it plugged in to APC so i can see how many volts going in or out and other info that APC displays!

Thanks for all suggestions!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:12 AM

0 Likes
0
1709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:47 AM . Last Modified: ‎2024-03-22 01:12 AM

I understand that, keep in mind that I'm connecting it to the car battery not outlet in my house.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore