APC Back-UPS ES 500 shutting down in 5 minutes when 2 5V devices connected.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC Back-UPS ES 500 shutting down in 5 minutes when 2 5V devices connected.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:26 PM . Last Modified: ‎2024-03-21 02:55 AM

0 Likes
8
2854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 PM . Last Modified: ‎2024-03-21 02:55 AM

APC Back-UPS ES 500 shutting down in 5 minutes when 2 5V devices connected.

I have a APC Back-UPS ES 500.

I have connected two 5V powered devices to it (to the battery backup available sockets). When there is a power outage, UPS shutdown in exact 5 minutes. No low battery warning. It act as the same way when there is no load.

How to fix it?

Thanks,
Simon Mandy

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 5
  • 500
  • 5v
  • apc
  • back-ups
  • es
  • minutes
  • shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:26 PM . Last Modified: ‎2024-03-21 02:54 AM

0 Likes
0
2855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 PM . Last Modified: ‎2024-03-21 02:54 AM

Simon,

Can you provide the exact scenario that you are experiencing? Is the UPS shutting down after it has ran on battery for 5 minutes or only when there is 5 minutes runtime left? Do you have a PC connected thru the UPS communication cable as well as PowerChute Personal Edition?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:27 PM . Last Modified: ‎2024-03-21 02:54 AM

0 Likes
0
2854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:27 PM . Last Modified: ‎2024-03-21 02:54 AM

Is there anyway to change this setting? In case of a power outage, I want UPS to be running till the battery drains. Equipment I am going to connect would be just a 5V 2A, AC to DC adapter.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:26 PM . Last Modified: ‎2024-03-21 02:54 AM

0 Likes
0
2856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 PM . Last Modified: ‎2024-03-21 02:54 AM

Simon,

Can you provide the exact scenario that you are experiencing? Is the UPS shutting down after it has ran on battery for 5 minutes or only when there is 5 minutes runtime left? Do you have a PC connected thru the UPS communication cable as well as PowerChute Personal Edition?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:26 PM . Last Modified: ‎2024-03-21 02:54 AM

0 Likes
0
2854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 PM . Last Modified: ‎2024-03-21 02:54 AM

My UPS is connected to a Raspberry Pi using the USB port. OS is Debian based Linux and software used to manage UPS is apcupsd. Raspberry is powered using one of the Power points from UPS. Raspberry Pi's power adapter is 5V 2A AC- DC adapter.
When there is a power outage, in exact 5 minutes UPS gets shutdown. No low battery alarm. I am sure its not because of low battery. If I connect a normal PC it will run for more than 10 minutes before it beeps for low battery.
Its acting as there is no load on the ups, and it shutdown after 5 minutes thinking there is no load.

Thanks,
Simon Mandy

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:27 PM . Last Modified: ‎2024-03-21 02:54 AM

0 Likes
0
2854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:27 PM . Last Modified: ‎2024-03-21 02:54 AM

I am not too familiar with regards to the configuration of APCUPSD, have you tried seeking help from them if there's any setting that needs to be changed?

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 07:27 PM . Last Modified: ‎2024-03-21 02:54 AM

0 Likes
0
2854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:27 PM . Last Modified: ‎2024-03-21 02:54 AM

>
Its acting as there is no load on the ups, and it shutdown after 5 minutes thinking there is no load.
>

I think you're right; BackUPS will shut down and conserve battery if there's no load. The Model B uses 3.5W at most.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:27 PM . Last Modified: ‎2024-03-21 02:54 AM

0 Likes
0
2855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:27 PM . Last Modified: ‎2024-03-21 02:54 AM

Is there anyway to change this setting? In case of a power outage, I want UPS to be running till the battery drains. Equipment I am going to connect would be just a 5V 2A, AC to DC adapter.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 07:27 PM . Last Modified: ‎2024-03-21 02:54 AM

0 Likes
0
2854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:27 PM . Last Modified: ‎2024-03-21 02:54 AM

I don't think there's any way to adjust this. The SmartUPS UPSes will run on battery until they are depleted, but they're somewhat bigger and heavier than a BackUPS. I don't know if there's any BackUPS that will stay on at low load.

Perhaps run your Raspberry Pi on batteries? A DC backup like this or straight from batteries as described here.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:27 PM . Last Modified: ‎2024-03-21 02:54 AM

0 Likes
0
2854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:27 PM . Last Modified: ‎2024-03-21 02:54 AM

There is a setting in Powerchute to make the untit shut down after exactly 5 minutes.  Connect to your ES 500  with Power chute and see if you can modify it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:27 PM . Last Modified: ‎2024-03-21 02:54 AM

0 Likes
0
2854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:27 PM . Last Modified: ‎2024-03-21 02:54 AM

I also face exactly similar issue with my ES500. The LED alternates between GREEN & RED on the shutdown. Any method to disable this autoshutdown feature? BTW, I don't have the Powerchute Software with me and the method to configure the UPS. Any help in this regard, please ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of