APC Back-UPS 600 - Long beep and no lights when there is a power outage, does not provide battery power

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC Back-UPS 600 - Long beep and no lights when there is a power outage, does not provide battery power
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
johanfeliz08
johanfeliz08
Cadet

Posted: ‎2024-08-29 05:29 PM . Last Modified: ‎2024-08-29 05:40 PM

0 Likes
4
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-29 05:29 PM . Last Modified: ‎2024-08-29 05:40 PM

APC Back-UPS 600 - Long beep and no lights when there is a power outage, does not provide battery power

The software says the battery is ok, but when there is a power outage the APC just goes off and start a long beep with no lights even if there is no device plugged in, after the power outage i check the battery charge and stays the same, i don't know why is not providing battery power. (Also i did a self test in the software and it passed)

 

Battery status:

johanfeliz08_0-1724977421927.png

General status:

johanfeliz08_1-1724977435080.png

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Teken
Kirk Teken
Kirk

Posted: ‎2024-08-30 02:23 PM

0 Likes
3
1420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-30 02:23 PM

The service life of the internal battery cartridge is 2-5 years based on usage, temperature, and environmental conditions. 

APC recommends the internal battery be replaced at the three year interval. Based on your image capture your battery is four years old.

 

The constant tone from the system indicates the battery needs to be replaced.


  • You can replace the battery with any quality cell that is HA rated. Consider spending the extra finances on a 9 AH cell vs 7.5 AH as it will provide longer operational runtime when needed.

 

Once the battery has been replaced insure you update the battery installation date. Doing so will reset the internal counters and may also adjust the charging tables.

 

You’ll want to manually initiate a Self Test and let it pass and recharge. Complete the last stage by manually initiating a battery calibration with at least 30% attached load.

 

Let the system recharge the new cell back to 100% SOC. The APC PCPE Software will than be more reflective of the operational runtime available. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

johanfeliz08
johanfeliz08
Cadet

Posted: ‎2024-08-31 03:24 PM

In response to Teken
0 Likes
2
1372
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-31 03:24 PM

I was checking after i posted this and I realized that when there is a power outage the system indicates that the device is overloaded even with no devices connected, does this change anything? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-09-02 05:32 AM

In response to johanfeliz08
0 Likes
1
1360
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-02 05:32 AM

If the hardware is still covered by APC Warranty please contact them for a RMA. If the hardware is not in warranty you may consider a brain Dead reset:

 

https://www.apc.com/us/en/faqs/FA156611/

 

Power down and disconnect all loads. Disconnect AC Mains from the wall outlet. Disconnect the internal battery cartridge. Press and hold the power button until you hear a click / beep.

 

You may not hear anything at all either! ☝️

 

Reconnect everything including the USB cable that is running APC Power Chute Software.

 

Do not connect any loads to the system. Power on the system and let it complete the Self Test (POST).

 

What are the results and is there any active faults / error codes displayed?!? Keep in mind the battery should have been replaced as doing all of the above is just wasting time. 

Reply

Link copied. Please paste this link to share this article on your social media post.

johanfeliz08
johanfeliz08
Cadet

Posted: ‎2024-09-05 12:31 AM

In response to Teken
0 Likes
0
1334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-05 12:31 AM

After i did the brain dead reset, when i turn it on the power light is flashing green for some seconds and then the light turns flashing red with a long beep, so it looks like as you said its the battery, and the software was showing the battery's status wrong. (i can't get the status on the APC software because i uninstalled it and now it does not recognize the UPS and i can't install it.) Thank you so much for your time and help. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore