Brand new 400VA ES charged for a week then tested supporting two ADSL modems (draw 12W in total). Runtime achieved only 55 minutes. APC website UPS Selector tool claims 125 minutes for this load. Have I bought the wrong unit? Would changing to 650VA or more increase runtime?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-23 02:09 AM
Hi @Anonymous user
Thank you for reaching out to the SE Community, my name is Jon and I will assist you with this query. May I please know the model number of the UPS?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-23 04:16 PM
From the runtime graph that I was able to find here, it shows that the minimum load is 45W with a runtime of 1 hour and 26 minutes. In my experience, this has something to do with the low load that is attached to the UPS.
Have you tried charging the UPS to 100% and letting it run on battery without anything connected?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-11-27 06:32 AM
Hi Jon
Ran the experiment you suggested. 100% charged runtime 51 minutes with zero load. Is this a faulty unit?
Checked router load while I was at it. I need 13W back up for as long as possible. What product should I choose if the 400 ES is unsuitable?
Graeme
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-12-05 11:11 PM
Apologies for the late revert @Anonymous user. Is it possible for you to add more load on the UPS? I am thinking that due to a very low load that the UPS is behaving that way.
Link copied. Please paste this link to share this article on your social media post.