APC BE550G battery backup problem

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC BE550G battery backup problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
125
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-22 02:21 AM

0 Likes
5
2101
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-22 02:21 AM

APC BE550G battery backup problem

Hi, I recently got a APC BE550G to protect my computer from power outtages. It goes on to battery backup fine when I unplug it from the wall however my main source of power is a generator so I often run out of power and whenever this happens my apc switchs to battery backup but my computer still loses power before it does. I also have a external hard drive plugged into the apc and when this happens it does not lose power before the apc switch's to battery backup and it works fine. I thought maybe it was a falty unit and I exchanged it for a new one but I still have the same problem. I also Thought maybe The battery charge was just running out but every time I check it it says around 90 to 100 percent charged. Any Suggestions?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-22 02:21 AM

0 Likes
0
2100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-22 02:21 AM

Does the UPS stay on during this whole process, or does it turn off along with your PC? What exactly happens when your batteries run out of power? Is the generator always on, or does it take a few minutes to kick on...?

My guess at this point is that, whatever happens when your batteries turn off, your computer's power supply doesn't like it.

The UPS could be switching between online & on battery a couple of times during this transition from battery to generator power, which probably makes your computer's power supply freak out. Multiple transfers, in addition to the longer transfer time required for use with the generator, is more difficult for your power supply to handle than a direct and single UPS transition from online to on battery, which you said it handles fine.

Also, the UPS you have is the one with the longest transfer time, so you'd likely have better results with a higher end UPS. It's possible all you'd need is a [Back-UPS RS|http://www.apc.com/products/family/index.cfm?id=23], though depending on conditions, you may need to go to a [Smart-UPS|http://www.apc.com/products/family/index.cfm?id=165] model.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-22 02:21 AM

0 Likes
0
2100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-22 02:21 AM

Did you change anything for the unit to operate on generator power? You'd probably need to change the sensitivity settings to allow the UPS to accept the generator power (it tends to fluctuate a lot, which a UPS doesn't like), though that also increases the length of the transfer time, which may be too long for your computer's power supply. It's a different power supply from your hard drive, which is probably more durable in terms of transfer time.

Also, it's not entirely relevant, but how is your main source of power a generator? Are you saying you don't have any utility power?

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-22 02:21 AM

0 Likes
0
2099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-22 02:21 AM

Josha,

I would like to gather some more information from you to provide you ideas to fix this issue. Is the Computer plugged into the battery backup outlet? Could you please let us know the exact model number of the Computer? What is the estimated runtime showing on Power Chute software? Is the Computer rebooting or shutting down when this happens?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-22 02:21 AM

0 Likes
0
2099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-22 02:21 AM

Thx for the reply. The computer is a custom built one the same as this one -- http://cgi.ebay.com/AMD-QUAD-X4-PHENOM-II-955-AM3-COMPUTER-SYSTEM-PC-NEW_W0QQitemZ110498955959QQcmdZ...
The estimated battery time in powerchute is showing up as 14 minutes and the computer just completely loses power and does not reboot.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-22 02:21 AM

0 Likes
0
2099
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-22 02:21 AM

Thx for replying. I had to change the sensitivity setting to low otherwise I would get a loud clicking sound every second. and yeah all my power comes from a generator and solar panels that charge some batterys. The thing I don't get about it not being able to switch over fast enough is whenever I manually stop power from going to it by unplugging it or turning of my power it works fine and my computer stays on. it just when my batterys shut off because theres not enough power in them that it my computer loses power.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-22 02:21 AM

0 Likes
0
2101
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:41 AM . Last Modified: ‎2024-03-22 02:21 AM

Does the UPS stay on during this whole process, or does it turn off along with your PC? What exactly happens when your batteries run out of power? Is the generator always on, or does it take a few minutes to kick on...?

My guess at this point is that, whatever happens when your batteries turn off, your computer's power supply doesn't like it.

The UPS could be switching between online & on battery a couple of times during this transition from battery to generator power, which probably makes your computer's power supply freak out. Multiple transfers, in addition to the longer transfer time required for use with the generator, is more difficult for your power supply to handle than a direct and single UPS transition from online to on battery, which you said it handles fine.

Also, the UPS you have is the one with the longest transfer time, so you'd likely have better results with a higher end UPS. It's possible all you'd need is a [Back-UPS RS|http://www.apc.com/products/family/index.cfm?id=23], though depending on conditions, you may need to go to a [Smart-UPS|http://www.apc.com/products/family/index.cfm?id=165] model.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore